Hi

I have a problem with my two way s gang dimmer switches for the hall and landing lights. I used to have normal on/off switches downstairs and up, this seemed to work fine.
When I replaced them with two two-way dimmers things started to go wrong.

Downstairs I have 3 wires: red, yellow (with red band) and blue. For the same light but on the upstairs switch I have 5 wires: red (x2), black (with red band), yellow and blue. I have identified what I think is the constant live at both ends.

The best I can get is a low glow on the upstairs light, no dimming and no control whatsoever from the downstairs switch!

Can anybody please help me with this?

Thanks very much,

Andy
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
il78

from United Kingdom

Joined: 06 Oct 2003
Posts: 701
Location: United Kingdom

PostPosted: Wed Nov 12, 2003 11:01 am Reply with quote

I take it that the hallway light is working fine on the dimmer……

At the hallway switch:
3 Core cable RED/YELLOW/BLUE
YELLOW to C
RED to L1
BLUE to L2

At landing switch:
3 Core cable and 2 Core cable RED/YELLOW/BLUE & RED/BLACK
YELLOW to C
RED & RED to L1
BLUE & BLACK to L2

All earths to brass terminals

I have been informed that 2 dimmers in circuit will not operate, so you must have a normal switch installed somewhere (ie, upstairs)
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 48586
Location: London,
United Kingdom
Thanked: 1838 times

PostPosted: Wed Nov 12, 2003 11:24 am Reply with quote

I take it you have bought proper multi-way dimmers, with a master/slave relationship, or some sort of intelligent control link between them?

Not just dimmers that have 2-way switching capability so that you can have ONE dimmer in place of ONE 2-way switch?

If not, you're *****d, as you can't have 2 conventional dimmers in series.
Back to top
 Alert Moderators
ajstant

from United Kingdom

Joined: 12 Nov 2003
Posts: 3
Location: United Kingdom

PostPosted: Wed Nov 12, 2003 1:53 pm Reply with quote

Both dimmers (upstairs and downstairs) are 2 gang 2 way switches. To be honest I didn't know they wouldn't be 'professional'.

This means I can't do what I want then I presume? icon_sad.gif What will happen, nothing or something? icon_question.gif

Why won't two dimmers work in series then?
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 48586
Location: London,
United Kingdom
Thanked: 1838 times

PostPosted: Wed Nov 12, 2003 3:22 pm Reply with quote

ajstant wrote:
Both dimmers (upstairs and downstairs) are 2 gang 2 way switches. To be honest I didn't know they wouldn't be 'professional'.

It's nothing to do with them being professional - they could be the finest product in the world, but they still wouldn't be able to do what they weren't designed to do. Did they come with a wiring diagram which led you to believe that you could have two in the same circuit?

Quote:
This means I can't do what I want then I presume? icon_sad.gif What will happen, nothing or something? icon_question.gif

What will happen is what's happening now.

Quote:
Why won't two dimmers work in series then?

Because even if they were simple potentiometers their resistance values would add up, making the final voltage output very low. As they aren't but are semiconductor switching circuits then what will almost certainly happen is that the output from the first dimmer will not be enough to trigger any functionality in the second.

But even if they were simple pots, nobody with even a modicum of knowledge of how two way lighting circuits work (i.e. which wires carry current and when, depending on relative switch positions), or of what voltage, current and resistance are would ever expect to be able to put 2 dimmers in series.

Are you sure you are up to this?
Back to top
 Alert Moderators
breezer

from United Kingdom

Joined: 03 Jan 2003
Posts: 23328
Location: Sussex,
United Kingdom
Thanked: 27 times

PostPosted: Wed Nov 12, 2003 6:36 pm Reply with quote

i think itt is a case of he didn't know you cant have two ordainairy dimmers controling the same circuit. after all it doesnt say on the box, that no one reads that you can't
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 48586
Location: London,
United Kingdom
Thanked: 1838 times

PostPosted: Wed Nov 12, 2003 10:58 pm Reply with quote

Ah - maybe it's just me, but even if you don't know how they work, (and I don't, precisely), surely it must be obvious that what you have is a little box where you put 240V in at one end and get less than that out at the other end, which is why your light is less bright. And that if you then take that "less than", and feed it INTO another one of the magic boxes, you'll get so little out that the light won't work at all?

But apparently not.

I've never fancied a dimmer at one end of a two-way switch circuit, as I just know that I'd always be at the wrong end when I wanted to adjust the wick, so I've never looked at "2-way" dimmers - do they really not have a diagram showing 1 dimmer and 1 switch?
Back to top
 Alert Moderators
Scoby_Beasley

from United Kingdom

Joined: 01 May 2003
Posts: 1880
Location: Durham,
United Kingdom
Thanked: 50 times

PostPosted: Wed Nov 12, 2003 11:23 pm Reply with quote

ban-all-sheds wrote:
do they really not have a diagram showing 1 dimmer and 1 switch?

Totally agree
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Problems connecting a 2 gang dimmer 2 640 Tue Jul 03, 2007 11:38 am
triple gang 2 way switch problems 3 380 Sat Jul 05, 2008 11:34 am
2 gang switch problems 6 640 Thu Apr 08, 2004 1:36 pm
Having Problems wiring 3 Gang and one 2 way switch 28 2980 Tue Jul 01, 2008 3:04 pm
2 way gang 2 way switch problems 3 740 Sat Apr 09, 2005 9:04 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.