PostPosted: Tue Apr 11, 2006 6:14 pm    Post Subject:
Faulty Circuit Breaker?
Reply with quote Thanks

I have been having trouble with my AC unit. Occasionally, the breaker flips and I have to reset it. I have had an AC company come out to look at the unit 5 times now and they still can not pinpoint an AC problem. I am starting to think it is the circuit breaker itself. How can I determine if the breaker is the culprit and needs to be replaced? The AC company is only interested in selling me AC parts. Today they decided that I may be leaking freon!!!! The system cools just fine when it runs and it will run for days without flipping!!
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16480
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Tue Apr 11, 2006 10:37 pm    Post Subject:
Reply with quote Thanks

Try posting in the Electrics outside UK!

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Tue Apr 11, 2006 10:53 pm    Post Subject:
Reply with quote Thanks

If I thought I had a faulty MCB, I'd just fit a new one. SP MCB is about £5 over here.

It's very unusual, though. I've heard the Chinese manufacturers, including counterfeit, can be very poor quality. I've known UK manufacture, such as Crabtree C50, run faultlessly for 40 years.

I wouldn't consider the MCB to be faulty before I'd compared the rating of the MCB with the rating on the AC unit, verified that there was no other load on the circuit, had a look for signs of overheating including damaged cables or rainwater/condensate causing a short.

I might also try a clamp meter to look at the actual current draw and compare to the AC rating; and I'd look up the manufacturer's documentation to see if they recommend a surge-resistant "slow-blow" type C or greater MCB to accommodate start-up surge.

What current does the maker's rating plate on the AC unit say, and what rating and type is your MCB?

What other loads are on the circuit?
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Faulty Earth on lighting circuit 4 400 Thu Sep 07, 2006 8:50 am
Has Faulty Kettle Damaged Electrical Circuit? 3 480 Mon Jun 05, 2006 2:50 pm
Faulty circuit? 24 1060 Sat Aug 05, 2006 9:06 pm
Faulty Circuit While Replacing Light Bulb 21 620 Sat Dec 30, 2006 4:08 pm
faulty ring circuit 4 1860 Fri Apr 06, 2007 7:24 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.