Joined: 31 Mar 2006 Posts: 6 Location: United Kingdom Thanked: 0 times
|
Posted: Sun Apr 16, 2006 12:09 pm Post Subject: central heating |
 |
|
just built a two story extention...is it ok to connect to the central heating radiator circiut on the existing upstairs into the new part upstairs then run it down into the new extention downstairs or is it best to go upstairs to upstairs and lower to lower?...does it matter ?..thanks for any replies |
|
croydoncorgi

Joined: 06 Jun 2004 Posts: 1642 Location: London, United Kingdom Thanked: 0 times
|
Posted: Sun Apr 16, 2006 12:22 pm Post Subject: |
 |
|
Bit late in the design process to think about this!
Have you actually checked what pipe sizes run to where?
How many rads in the new bits?
If you connect the new downstairs rads to the upstairs circuit, you may run out of pipe capacity and / or operating pressure, so no heat will get downstairs.
But most 'conventional' heating systems have the pump upstairs, next to the cylinder anyway. Where's yours?
Also, depending on the size of the house, Building Regs demand separate upstairs and downstairs zones. Even if your (enlarged) house is not that big, it might still be a good idea to zone it. |
|
naylor

Joined: 31 Mar 2006 Posts: 6 Location: United Kingdom Thanked: 0 times
|
|
croydoncorgi

Joined: 06 Jun 2004 Posts: 1642 Location: London, United Kingdom Thanked: 0 times
|
Posted: Sun Apr 16, 2006 3:12 pm Post Subject: |
 |
|
Yes - but what boiler is it? Combi? system boiler? where's the pump? what size of pipe are youb planning to connect TO? |
|
naylor

Joined: 31 Mar 2006 Posts: 6 Location: United Kingdom Thanked: 0 times
|
Posted: Sun Apr 16, 2006 5:25 pm Post Subject: |
 |
|
its a combi(potterton performa 30he) i presume the pumps in the boiler?..was just gonna branch off the existing pipe work which is 15mm |
|