3kw built in cooker
I have bought a 3kw built in cooker to replace a gas cooker. The gas hob is staying and its ignition works via a 13amp plug.
Distance from cooker to consumer unit is approx 15m. Instruction booklet suggests fuse of a min 15amps and max 20amps with min 2.5mm cable and a double pole switch between cooker and consumer unit. Can you advise as I don't seem to be able to find a double pole switch in the local DIY less than 45amps for a cooker and I would have thought I would need a heavier cable over 15m. Despite instructions should I fit a 45 amp double pole switch and join consumer unit at a vacant 45amp fuse?
Joined: 30 Apr 2006 Posts: 13 Location: United Kingdom Thanked: 0 times
Posted: Sun Apr 30, 2006 8:30 pm Post Subject:
3kw built in cooker
Thanks for the quick reply. When you say "A switched spur is a double pole switch", am I to presume you mean the spur for the hob? This is only 13amp and although I am led to believe a 13amp takes 3kw as a maximum the instruction book says different. Sorry to be pedantic, but can you be a little clearer and describe the cable, switch and fuse connections and sizes? I'll certainly search again for a 20A double pole switch since you say they should have one.
Joined: 31 Mar 2006 Posts: 10752 Location: Birmingham, United Kingdom Thanked: 73 times
Posted: Sun Apr 30, 2006 8:48 pm Post Subject:
A Switched spur is just a D.P. switch with the addition of an integral fuse.
You will be fine running the cable in 2.5mm2 T+E Providing there are no derating factors to take into accout (i.e. running the cable in thermal insulation etc) This can then be connected to a 16A MCB in your consumer unit.
The cooker end can either be connected via a 13A switched spur(Click Here) or via a 20A double pole switch (Click here)
Are you aware that this work needs to be notified to your local authority building control?
Joined: 30 Apr 2006 Posts: 13 Location: United Kingdom Thanked: 0 times
Posted: Sun Apr 30, 2006 10:41 pm Post Subject:
3kw built in cooker
Thanks Rob.
So, thats a 2.5mm2 T+E from cooker to terminal outlet box (you didn't say, but I assume I'll need one?), then the same cable to the DP switch (13A switched spur or a 20A DP), then the same cable to a 16A MCB in the consumer unit.
I'll be using plastic conduit to route the cable to minimise damage to decor (again I assume this is ok?) and there's no thermal insulation to worry about, but I didn't know about building control!
Joined: 17 Feb 2004 Posts: 697 Location: United Kingdom Thanked: 0 times
Posted: Mon May 01, 2006 6:35 pm Post Subject:
thoretically 2.5 should be OK, and if you take in consideration diversity factor it is even better, but you have to be very careful and note this somewhere you don't know what kind of cooker the next person will buy.
As I understand this is a new circuit; cable, MCB, FS etc to TMHO it is notifyable work.
__________________ I'm not in a mental institute... just a house for the insane
Joined: 30 Apr 2006 Posts: 13 Location: United Kingdom Thanked: 0 times
Posted: Mon May 01, 2006 7:32 pm Post Subject:
3kw built in cooker
Its in and working so thanks for the help. Also added an earth to the consumer unit as per instructions on the switch, etc. Not sure why though with 2c+e cable throughout!?
Joined: 30 Apr 2006 Posts: 13 Location: United Kingdom Thanked: 0 times
Posted: Tue May 02, 2006 4:49 pm Post Subject:
3kw built in cooker
Additional earth from the terminal outlet box to the DP switch and from the DP switch to the consumer unit attached to the tob and DP switch earth connectors according to instructions. As I say cooker is working so hope this is just excessive at worst and necessary at best.
Joined: 30 Apr 2006 Posts: 13 Location: United Kingdom Thanked: 0 times
Posted: Tue May 02, 2006 6:41 pm Post Subject:
3kw built in cooker
That may be so, but the leaflets (as with the DP switch and tbo) came with the instructions printed and produced by Wickes and Homebase respectively (British companies, I believe) clearly showing and describing the need to have an additional earth wire to the consumer unit for both items.
Joined: 31 Mar 2006 Posts: 10752 Location: Birmingham, United Kingdom Thanked: 73 times
Posted: Tue May 02, 2006 6:48 pm Post Subject:
Seems a little over the top, but better safe than sorry. Is there any chance you can scan / photograph the leaflet just to endulge my curiosity (or I won't sleep tonight)
Joined: 31 Mar 2006 Posts: 10752 Location: Birmingham, United Kingdom Thanked: 73 times
Posted: Wed May 03, 2006 7:31 pm Post Subject:
You will need to use an image hoster such as photobucket.com
You upload the image to their site and they provide you with the line of text you need to post in the forum (in the Img box)
If this is too much hassle you can email it to me and I will post it.
You cannot post new topics in this forum You cannot reply to topics in this forum You cannot edit your posts in this forum You cannot delete your posts in this forum You cannot vote in polls in this forum