3kw built in cooker

This topic originated from the How to page called Choosing the correct size cable
Click here to return to the page called Choosing the correct size cable.
Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
RPP

from United Kingdom

Joined: 30 Apr 2006
Posts: 13
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Apr 30, 2006 7:54 pm    Post Subject:
3kw built in cooker
Reply with quote Thanks

I have bought a 3kw built in cooker to replace a gas cooker. The gas hob is staying and its ignition works via a 13amp plug.

Distance from cooker to consumer unit is approx 15m. Instruction booklet suggests fuse of a min 15amps and max 20amps with min 2.5mm cable and a double pole switch between cooker and consumer unit. Can you advise as I don't seem to be able to find a double pole switch in the local DIY less than 45amps for a cooker and I would have thought I would need a heavier cable over 15m. Despite instructions should I fit a 45 amp double pole switch and join consumer unit at a vacant 45amp fuse?
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Sun Apr 30, 2006 8:16 pm    Post Subject:
Reply with quote Thanks

A switched spur is a double pole switch, also they should stock a 20A double pole switch (commonly used on water heater circuits)

HTH

Rob
Back to top
 Alert Moderators
RPP

from United Kingdom

Joined: 30 Apr 2006
Posts: 13
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Apr 30, 2006 8:30 pm    Post Subject:
3kw built in cooker
Reply with quote Thanks

Thanks for the quick reply. When you say "A switched spur is a double pole switch", am I to presume you mean the spur for the hob? This is only 13amp and although I am led to believe a 13amp takes 3kw as a maximum the instruction book says different. Sorry to be pedantic, but can you be a little clearer and describe the cable, switch and fuse connections and sizes? I'll certainly search again for a 20A double pole switch since you say they should have one.
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Sun Apr 30, 2006 8:48 pm    Post Subject:
Reply with quote Thanks

A Switched spur is just a D.P. switch with the addition of an integral fuse.
You will be fine running the cable in 2.5mm2 T+E Providing there are no derating factors to take into accout (i.e. running the cable in thermal insulation etc) This can then be connected to a 16A MCB in your consumer unit.
The cooker end can either be connected via a 13A switched spur(Click Here) or via a 20A double pole switch (Click here)

Are you aware that this work needs to be notified to your local authority building control?

Rob
Back to top
 Alert Moderators
RPP

from United Kingdom

Joined: 30 Apr 2006
Posts: 13
Location: United Kingdom
Thanked: 0 times

PostPosted: Sun Apr 30, 2006 10:41 pm    Post Subject:
3kw built in cooker
Reply with quote Thanks

Thanks Rob.

So, thats a 2.5mm2 T+E from cooker to terminal outlet box (you didn't say, but I assume I'll need one?), then the same cable to the DP switch (13A switched spur or a 20A DP), then the same cable to a 16A MCB in the consumer unit.

I'll be using plastic conduit to route the cable to minimise damage to decor (again I assume this is ok?) and there's no thermal insulation to worry about, but I didn't know about building control!

PS thanks for the links.
Back to top
 Alert Moderators
Albert

from United Kingdom

Joined: 17 Feb 2004
Posts: 697
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon May 01, 2006 6:35 pm    Post Subject:
Reply with quote Thanks

thoretically 2.5 should be OK, and if you take in consideration diversity factor it is even better, but you have to be very careful and note this somewhere you don't know what kind of cooker the next person will buy.

As I understand this is a new circuit; cable, MCB, FS etc to TMHO it is notifyable work.

__________________
I'm not in a mental institute... just a house for the insane
Back to top
 Alert Moderators
RPP

from United Kingdom

Joined: 30 Apr 2006
Posts: 13
Location: United Kingdom
Thanked: 0 times

PostPosted: Mon May 01, 2006 7:32 pm    Post Subject:
3kw built in cooker
Reply with quote Thanks

Its in and working so thanks for the help. Also added an earth to the consumer unit as per instructions on the switch, etc. Not sure why though with 2c+e cable throughout!?
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12845
Location: Yorkshire,
United Kingdom
Thanked: 21 times

PostPosted: Tue May 02, 2006 3:18 pm    Post Subject:
Re: 3kw built in cooker
Reply with quote Thanks

RPP wrote:
Also added an earth to the consumer unit as per instructions on the switch, etc. Not sure why though with 2c+e cable throughout!?

What exactly did the instructions say regarding this? . . . icon_eek.gif
Back to top
 Alert Moderators
RPP

from United Kingdom

Joined: 30 Apr 2006
Posts: 13
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue May 02, 2006 4:49 pm    Post Subject:
3kw built in cooker
Reply with quote Thanks

Additional earth from the terminal outlet box to the DP switch and from the DP switch to the consumer unit attached to the tob and DP switch earth connectors according to instructions. As I say cooker is working so hope this is just excessive at worst and necessary at best.
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Tue May 02, 2006 5:35 pm    Post Subject:
Reply with quote Thanks

Instructions probably intended for some inferior country with two-pin plugs.
Back to top
 Alert Moderators
RPP

from United Kingdom

Joined: 30 Apr 2006
Posts: 13
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue May 02, 2006 6:41 pm    Post Subject:
3kw built in cooker
Reply with quote Thanks

That may be so, but the leaflets (as with the DP switch and tbo) came with the instructions printed and produced by Wickes and Homebase respectively (British companies, I believe) clearly showing and describing the need to have an additional earth wire to the consumer unit for both items.
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Tue May 02, 2006 6:48 pm    Post Subject:
Reply with quote Thanks

Seems a little over the top, but better safe than sorry. Is there any chance you can scan / photograph the leaflet just to endulge my curiosity (or I won't sleep tonight) icon_biggrin.gif

Rob
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Tue May 02, 2006 10:13 pm    Post Subject:
Re: 3kw built in cooker
Reply with quote Thanks

RPP wrote:
That may be so, but the leaflets (as with the DP switch and tbo) came with the instructions printed and produced by Wickes and Homebase respectively

more likely printed and produced by whatever chineese brand wickes and homebase are rebranding..........................
Back to top
 Alert Moderators
RPP

from United Kingdom

Joined: 30 Apr 2006
Posts: 13
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed May 03, 2006 7:18 pm    Post Subject:
3kw built in cooker
Reply with quote Thanks

Rob - I have a scanner, but not clear how I insert the image (not as clever as some of you out there). Can you guide me?
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Wed May 03, 2006 7:31 pm    Post Subject:
Reply with quote Thanks

You will need to use an image hoster such as photobucket.com
You upload the image to their site and they provide you with the line of text you need to post in the forum (in the Img box)

If this is too much hassle you can email it to me and I will post it.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
replacement built in cooker 5 460 Wed Aug 10, 2005 9:42 pm
Installation of new built in cooker and hob 10 820 Mon Jan 22, 2007 5:15 pm
Removing built under cooker 4 2040 Sun Apr 01, 2007 9:46 am
installing a new built-in oven/cooker 16 420 Wed Jan 21, 2009 2:55 pm
plug socket sited directly behind built in cooker/microwave 2 460 Thu Apr 24, 2008 2:01 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.