I know diversity is perfectly allowable, but I would ignore it and plump for a circuit that can carry flc.
The Electrician's Guide to the Building Regulations gives a 6mm2 cable (CUU with s/o) suitable for carrying 32A for a maximum length of 40m. However, EFL must be no more than 1.2 (type B) or 1.5 (type 1).
10mm2 can be used for 40A circuit. Same max length applies. EFL 0.96 (B) and 1.2 (1).
Both these calculations are worked out on Installation Methods 1, 3, 4, 6, & 15.
Same situations as above, but with BS1361 fuse gives 42m max length and 0.96 Ohm for 30A circuit, and for the 45A circuit, 50m max length on PME and 10m on TN-S, both with max loops of 0.8.