eastweb

Joined: 30 May 2006 Posts: 2 Location: London, United Kingdom Thanked: 0 times
|
Posted: Tue May 30, 2006 12:17 pm Post Subject: Spur to outside socket |
 |
|
Hi.
I want to add an ip rated socket to the outside of my house for strimmer / mower type use and would like to spur off a socket from the kitchen ring main.
The ring is protected at the CU by an rcd so can i just simply drill a hole in the kitchen wall and connect (spur) the socket to the dishwasher socket??
Thanks for any help. |
|
Adam_151

Joined: 17 Jun 2004 Posts: 4538 Location: United Kingdom Thanked: 10 times
|
Posted: Tue May 30, 2006 12:39 pm Post Subject: |
 |
|
As long as the socket you wish to spur off is not a spur itself, or already serving a spur, then yes, but as the socket you wish to spur off is in the kitchen, then its definatly notifiable work (if it was not in the kitchen, its a bit more grey tbh) |
|
eastweb

Joined: 30 May 2006 Posts: 2 Location: London, United Kingdom Thanked: 0 times
|
Posted: Tue May 30, 2006 12:49 pm Post Subject: |
 |
|
Thanks mate.
Its not a spur just part of the existing ring and because its my house i'll notify the MRS of the work to be undertaken.
Cheers |
|