Earthing for new plumbing
Can someone please tell me what I need to earth in a new kitchen under the new regulations. We have just put in a new kitchen including plumbing and there is an existing earth wire from the main circuit board which I need to extend and connect to the new plumbing.
Joined: 17 Jun 2004 Posts: 4538 Location: United Kingdom Thanked: 10 times
Posted: Wed Jun 07, 2006 10:39 am Post Subject:
No cross bonding require in kitchens, metallic service pipes entering or leaving the property should be bonded with 10mm˛ to the MET within 600mm of entry and on the consumers side of any meters
Joined: 24 Jul 2007 Posts: 95 Location: United Kingdom Thanked: 0 times
Posted: Wed Jul 25, 2007 8:36 am Post Subject:
Earth Bonding
Adam_151 wrote:
No cross bonding require in kitchens, metallic service pipes entering or leaving the property should be bonded with 10mm˛ to the MET within 600mm of entry and on the consumers side of any meters
Hi what if your using all plastic fittings for all plumbing, should you still have to bond all kitchen matalic objects as with rads around hse,
Joined: 11 Jan 2007 Posts: 700 Location: United Kingdom Thanked: 0 times
Posted: Wed Jul 25, 2007 6:57 pm Post Subject:
Re: Earth Bonding
[quote="Mini1961"]
Adam_151 wrote:
Hi what if your using all plastic fittings for all plumbing, should you still have to bond all kitchen matalic objects as with rads around hse,
Metallic objects in kitchens no longer need bonding.
That is called supplementary bonding and now only refers to metallic objects in bathrooms.
However, if your mains water pipe (and gas) is copper,it needs bonding this side of the stop tap with 10mm˛ earthing cable.
That's called main equipotential bonding.
Joined: 24 Jul 2007 Posts: 95 Location: United Kingdom Thanked: 0 times
Posted: Wed Jul 25, 2007 10:11 pm Post Subject:
Re: Earth Bonding
[quote="luminaire"]
Mini1961 wrote:
Adam_151 wrote:
Hi what if your using all plastic fittings for all plumbing, should you still have to bond all kitchen matalic objects as with rads around hse,
Metallic objects in kitchens no longer need bonding.
That is called supplementary bonding and now only refers to metallic objects in bathrooms.
However, if your mains water pipe (and gas) is copper,it needs bonding this side of the stop tap with 10mm˛ earthing cable.
That's called main equipotential bonding.
Thanks
water plastic and gas not in yet i will have to bond it if i hear you right as with copper connectiion in to hot water tank, i am so surprised you do not have to bond the kitchen sink?