PostPosted: Wed Jul 05, 2006 5:49 pm    Post Subject:
ring circuit headroom reduced
Reply with quote Thanks

I have just tried to extend an existing ring circuit to add a new socket, but have run into problems. I located the ring cable, cut it and installed new cable to the new outlet and back again using 30A junction boxes. However as soon as i tried to run something from the new outlet the RCD at the consumer unit tripped. Assuming I had introduced a fault somewhere I then disconnected the new cable and connected the two junction boxes to restore the original loop, minus my new addition. However, although the circuit functions it still trips the RCD very easily if anything of reasonable power (eg. vacuum cleaner) is started. Before my meddling this circuit was very stable, never had any problems. It is not overloaded, only a PC and TV most of the time. Its as if the headroom has been reduced significantly, but I don't understand how that can be. If there's an earth fault or something on the circuit wouldn't the RCD refuse to re-set ? Grateful if someone could point me in the right direction on how to troubleshoot this.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Wed Jul 05, 2006 5:58 pm    Post Subject:
Reply with quote Thanks

Perhaps ypu have mis-connected the Neutral (black, or blue) and the Earth (green, green-and-yellow, or bare copper) together or touching each other, including perhaps in one of the steel back-boxes.

Have you sheathed all the earth wires?

Did you touch anything at the consumer unit?
Back to top
 Alert Moderators
Lanca

from United Kingdom

Joined: 26 Mar 2006
Posts: 8
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Jul 05, 2006 6:06 pm    Post Subject:
Reply with quote Thanks

Thanks for the prompt reply. I haven't touched any of the steel back boxes, all of the work was done in the loft. I have checked the wiring, brown to red and blue to black all seems ok. Can't see any nicks in the sheathing that might short, and yes I have sheathed the earths. Didn't touch anything at the consumer unit other than to re-set the RCD.
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6931
Location: United Kingdom
Thanked: 16 times

PostPosted: Wed Jul 05, 2006 8:17 pm    Post Subject:
Reply with quote Thanks

assuming all the new connections are correct and well made (no little metal tails etc) im guessing that your movement of the cable as you cut and joined it caused the fault.

you need to trace the cables from your new junction boxes to the existing sockets and look for any damage.

do the cables in question run down metal conduit in the wall? if so are the conduit ends digging into the cable (very common on diy rewires where the bulk of the conduit was ripped out but conduit in the walls left and T&E pulled through it)? entry points to sockets are also possiblly vulnerable.
Back to top
 Alert Moderators
bondy

from United Kingdom

Joined: 20 May 2006
Posts: 77
Location: Hertfordshire,
United Kingdom
Thanked: 0 times

PostPosted: Wed Jul 05, 2006 8:31 pm    Post Subject:
Reply with quote Thanks

have you checked the rcd?
Back to top
 Alert Moderators
Lectrician

from United Kingdom

Joined: 18 Jul 2004
Posts: 5167
Location: Devon,
United Kingdom
Thanked: 20 times

PostPosted: Wed Jul 05, 2006 9:18 pm    Post Subject:
Reply with quote Thanks

What else is protected by the RCD?
Back to top
 Alert Moderators
Lanca

from United Kingdom

Joined: 26 Mar 2006
Posts: 8
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Jul 05, 2006 10:10 pm    Post Subject:
Reply with quote Thanks

Thanks everyone for the help. I have disconnected everything once again and re-made the connections and everything seems ok at the moment. Hopefully it was just a dodgy connection somewhere, or I may have moved the cables fortuitously this time. I am still curious though why the RCD only tripped after a certain load was exceeded, shouldn't it trip automatically if there is a fault ?
Back to top
 Alert Moderators
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4541
Location: United Kingdom
Thanked: 10 times

PostPosted: Wed Jul 05, 2006 10:43 pm    Post Subject:
Reply with quote Thanks

Lanca wrote:
I am still curious though why the RCD only tripped after a certain load was exceeded, shouldn't it trip automatically if there is a fault ?


If there is a neutral->earth short, the additional load will drag the neutral away from earth voltage, creating a potential between neutral and earth which shunts a current through the fault and trips it, quite a few varaibles in it

The resistance of the fault
The neutral-> earth voltage normally (this willl vary throughout the day as loadings change)
How much more the neutral moves away from earth with the load you have applied (current of the load, and resistance of the conductors feeding it relevant here)
Etc, and because multiple circuits might be loaded and the fault is only one one, it becomes rather complicated if you wanted to calculate the leakage generated by this effect icon_smile.gif
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
HELP. Pendant light appears to have reduced power 13 320 Sun Aug 23, 2009 8:02 pm
Reduced average life of lightbulbs 7 480 Fri Mar 09, 2007 1:46 pm
Triton Opal Shower reduced power 5 1940 Sun Sep 24, 2006 7:59 am
Design of Ring Final Circuit 4 1320 Tue Aug 22, 2006 10:22 pm
Ring circuit extension or fused spur? 5 640 Fri Oct 20, 2006 12:53 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.