Posted: Thu Jul 20, 2006 1:19 pm Post Subject: Cable size |
 |
|
Hi Everyone
My lighting circuit is run on 1.5mm twin core and earth. However, I want to run 5 12v 50W spotlights (with transformers off JBs) in 1.0mm. Is it ok to do this or should I use 1.5mm?
Thanks |
|
ban-all-sheds

Joined: 27 Aug 2003 Posts: 21990 Location: London, United Kingdom Thanked: 78 times
|
Posted: Thu Jul 20, 2006 1:40 pm Post Subject: |
 |
|
What is the rating of the fuse/MCB on the lighting circuit? __________________ I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth. |
|
aidan1979

Joined: 20 Jul 2006 Posts: 28 Location: London, United Kingdom Thanked: 0 times
|
Posted: Thu Jul 20, 2006 3:43 pm Post Subject: |
 |
|
its a 6 AMP MCB. I think the JBs are 20A ones. |
|
ban-all-sheds

Joined: 27 Aug 2003 Posts: 21990 Location: London, United Kingdom Thanked: 78 times
|
Posted: Thu Jul 20, 2006 4:34 pm Post Subject: |
 |
|
1mm˛ will be fine on a 6A breaker, and will be fine for the load of these lights.
Just to be squeaky clean you should document the fact that you've put 1mm˛ in the circuit in case some future occupant decides to up the rating of the MCB on the basis of the existing 1.5mm˛ that he can see at the CU.... __________________ I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth. |
|
aidan1979

Joined: 20 Jul 2006 Posts: 28 Location: London, United Kingdom Thanked: 0 times
|
Posted: Thu Jul 20, 2006 4:43 pm Post Subject: |
 |
|
Good point. Thanks a lot for your advice! |
|