Electric supply to shed

This topic originated from the How to page called Types of electrical circuits
Click here to return to the page called Types of electrical circuits.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
cono

from United Kingdom

Joined: 02 Aug 2006
Posts: 14
Location: Norwich,
United Kingdom
Thanked: 0 times

PostPosted: Wed Aug 02, 2006 8:54 am    Post Subject:
Electric supply to shed
Reply with quote Thanks

Hi
I wish to take a supply to my shed. My interest is woodwork and sometime in the future I will be purchasing a bandsaw, the one I have in mind requires a 20amp supply. Plus the usual DIY tools such as a chop saw, router etc which will run from a 13amp supply.
The consumer unit which supplies electric to the house is in the garage. It is an old fashioned one, i.e. it uses rewireable fuse carriers, there are 6 in total, there are no spare fuseways. I guess it would be adviseable to change this with a modern one which also includes an RCD. Is it a good idea to use what I believe is called a split box?
The distance from existing consumer unit to shed is 24 mtrs.
I intend to use armoured cable buried 450mm deep with paving slabs over the top. In the shed I will have 4 flourescent lights and 6 double metal socket outlets, at any one time only the lights and one socket outlet will be in use. I intend a radial circuit for the socket outlets with a junction box feeding the lights.
What rating would be adviseable for the armoured cable?
I realise that I will have to comply with the latest regulations and will have the work checked by a qualified electrician who will I understand notify the appropriate body of the work carried out.
Any advice and recommendation will be greatfully received, many thanks for help. Apologies for a rather lengthy post, no doubt I will have missed something.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12845
Location: Yorkshire,
United Kingdom
Thanked: 21 times

PostPosted: Wed Aug 02, 2006 11:56 am    Post Subject:
Reply with quote Thanks

Given that you are having a dedicated 20A supply for one piece of equipment at the shed, i would recommend a submain of no less than 40A. This will require 10m² SWA and yes, you will need to change that outdated old wylex board in the garage.

please ask an electrician first, becaus it is actually illegal for them to sign off someone else's work. if your house burns down, they will get the blame because they put their name to your work. Also ask your local council building control for advice regarding complying with part p of the building regulations.
Back to top
 Alert Moderators
WabbitPoo

from United Kingdom

Joined: 26 Feb 2005
Posts: 893
Location: Nottingham,
United Kingdom
Thanked: 3 times

PostPosted: Wed Aug 02, 2006 7:21 pm    Post Subject:
Reply with quote Thanks

crafty1289 wrote:
This will require 10m² SWA .


M? isnt that a BIG cable? Forgive my ignorance of terminology if not, but should that be mm?
Back to top
 Alert Moderators
cono

from United Kingdom

Joined: 02 Aug 2006
Posts: 14
Location: Norwich,
United Kingdom
Thanked: 0 times

PostPosted: Wed Aug 02, 2006 7:55 pm    Post Subject:
Electric supply to shed
Reply with quote Thanks

crafty1289 wrote:
Given that you are having a dedicated 20A supply for one piece of equipment at the shed, i would recommend a submain of no less than 40A. This will require 10m² SWA and yes, you will need to change that outdated old wylex board in the garage.

please ask an electrician first, becaus it is actually illegal for them to sign off someone else's work. if your house burns down, they will get the blame because they put their name to your work. Also ask your local council building control for advice regarding complying with part p of the building regulations.


Crafty 1289
Many thanks for your helpful advice. Regarding the illegal aspect would it be OK if everything was made ready for the electrician, i.e. trench dug, socket outlets (backs) put where I require and the fluorescent lights placed in position but not connected? Also is it a good idea to have a split consumer unit when replacing my old one?
cono
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Wed Aug 02, 2006 8:17 pm    Post Subject:
Re: Electric supply to shed
Reply with quote Thanks

cono wrote:
Regarding the illegal aspect would it be OK if everything was made ready for the electrician, i.e. trench dug, socket outlets (backs) put where I require and the fluorescent lights placed in position but not connected?


Yep. No problem with that.
If you put a duct into the trench, then you could back fill the trench too.

I would recommend installing a duct, as this will allow you to replace the cable without the need to dig up the garden again, should you ever want a bigger supply, or in the unlikely event that the cable gets damaged.
If you do fit a duct don't forget to put a draw rope through to enable the cable to be drawn in.

Also it may be worth running a second duct to the shed, as now is the time while you have the trench up, even if you don't use it now, it will be there for the future. This will allow you to run things like a burglar alarm cable (not a bad idea with all those power tools), telephone, TV, internet etc.

Quote:
Also is it a good idea to have a split consumer unit when replacing my old one?


You will need to provide RCD protection to any socket outlets likely to supply equipment for use outdoors, and the most common way of doing this it to fit a split load board, but another way of acheiving this is to fit a standard consumer unit fitted with RCBOs to protect the sockets. This is a bit more of an expensive way to do things, but if a fault occours on one of the protected circuits, it will only trip the affected circuit, rather than a split load board which would cut the power to all the protected circuits.
Back to top
 Alert Moderators
cono

from United Kingdom

Joined: 02 Aug 2006
Posts: 14
Location: Norwich,
United Kingdom
Thanked: 0 times

PostPosted: Wed Aug 02, 2006 8:47 pm    Post Subject:
Re: Electric supply to shed
Reply with quote Thanks

RF Lighting wrote:
cono wrote:
Regarding the illegal aspect would it be OK if everything was made ready for the electrician, i.e. trench dug, socket outlets (backs) put where I require and the fluorescent lights placed in position but not connected?


Yep. No problem with that.
If you put a duct into the trench, then you could back fill the trench too.

I would recommend installing a duct, as this will allow you to replace the cable without the need to dig up the garden again, should you ever want a bigger supply, or in the unlikely event that the cable gets damaged.
If you do fit a duct don't forget to put a draw rope through to enable the cable to be drawn in.

Also it may be worth running a second duct to the shed, as now is the time while you have the trench up, even if you don't use it now, it will be there for the future. This will allow you to run things like a burglar alarm cable (not a bad idea with all those power tools), telephone, TV, internet etc.

Quote:
Also is it a good idea to have a split consumer unit when replacing my old one?


You will need to provide RCD protection to any socket outlets likely to supply equipment for use outdoors, and the most common way of doing this it to fit a split load board, but another way of acheiving this is to fit a standard consumer unit fitted with RCBOs to protect the sockets. This is a bit more of an expensive way to do things, but if a fault occours on one of the protected circuits, it will only trip the affected circuit, rather than a split load board which would cut the power to all the protected circuits.


RF Lighting
Thank you for your helpful advice. I shall certainly put ducts in, I intend to use either 40 or 50mm plastic pipe, the lengths connected with straight connectors. Will this be OK?
This is the first time that I have used a forum--hope I am responding to the posts giving me such helpful advice correctly.
cono
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Wed Aug 02, 2006 9:17 pm    Post Subject:
Reply with quote Thanks

40mm might be a bit on the small side, but 50mm should be fine. Try to keep joints to a minimum and avoid any tight bends as the cable may catch on these when being pulled in, which may result in having to redig part of the trench icon_mad.gif

Dont forget to put a strong rope in each duct.
Also you should put warning tape in the trench. 1 length just above the cables, and 1 length near the surface.




Buy it here
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Wed Aug 02, 2006 9:34 pm    Post Subject:
Re: Electric supply to shed
Reply with quote Thanks

RF Lighting wrote:

... another way of acheiving this is to fit a standard consumer unit fitted with RCBOs to protect the sockets. This is a bit more of an expensive way to do things, but if a fault occours on one of the protected circuits, it will only trip the affected circuit, rather than a split load board which would cut the power to all the protected circuits.


Well done that man!
Back to top
 Alert Moderators
toasty

from United Kingdom

Joined: 20 Sep 2004
Posts: 563
Location: Bristol,
United Kingdom
Thanked: 0 times

PostPosted: Thu Aug 03, 2006 9:21 am    Post Subject:
Reply with quote Thanks

10mm² ? Are you sure?

You can use 6mm² for a 40amp load up to 30 odd metres for pvc or xlpe and save your self a few quid not to mention the hassle of working with a thicker cable.

Crafty, I think you are confusing T&E with SWA.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16480
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Thu Aug 03, 2006 3:38 pm    Post Subject:
Reply with quote Thanks

I back Crafty. That way, you have future-proofed the installation.

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
toasty

from United Kingdom

Joined: 20 Sep 2004
Posts: 563
Location: Bristol,
United Kingdom
Thanked: 0 times

PostPosted: Thu Aug 03, 2006 3:57 pm    Post Subject:
Reply with quote Thanks

Agreed, future proofing is a good idea, but the point I'm making is that 40amp over 24meters doesn't require 10mm.

6mm is more than adequate.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16480
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Thu Aug 03, 2006 4:39 pm    Post Subject:
Reply with quote Thanks

Toasty - I don't have my regs with me - remind me what the VD values are for SWA multicore 6 & 10mm2...

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
cono

from United Kingdom

Joined: 02 Aug 2006
Posts: 14
Location: Norwich,
United Kingdom
Thanked: 0 times

PostPosted: Thu Aug 03, 2006 4:59 pm    Post Subject:
Electric supply to shed
Reply with quote Thanks

securespark wrote:
I back Crafty. That way, you have future-proofed the installation.


A big thanks to everyone on this forum for their comments. They are very, very helpful and have put me right to have everything done safely and future proof the installation-which is great! I shall start digging the trench soon, unfortunately I have to move a couple of trees and will have to wait until there dormant, but in the meantime can dig either side
cono
Back to top
 Alert Moderators
toasty

from United Kingdom

Joined: 20 Sep 2004
Posts: 563
Location: Bristol,
United Kingdom
Thanked: 0 times

PostPosted: Thu Aug 03, 2006 8:35 pm    Post Subject:
Reply with quote Thanks

securespark wrote:
Toasty - I don't have my regs with me - remind me what the VD values are for SWA multicore 6 & 10mm2...


Me neither, just use the TLC calculators, they are pretty good.

http://www.tlc-direct.co.uk/Technical/Charts/VoltageDrop.html
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
ELectric Supply to storage shed 6 560 Mon Dec 17, 2007 11:42 pm
Another Shed Supply Question With A Twist 41 1480 Fri May 30, 2008 9:15 pm
Supply to shed! 3 200 Tue Jun 24, 2008 10:07 pm
Additional supply to garden shed 6 340 Mon Jul 07, 2008 9:14 am
metal shed supply...earthing? 10 600 Sun May 11, 2008 10:00 am