Cable size to consumer unit

This topic originated from the How to page called Choosing the correct size cable
Click here to return to the page called Choosing the correct size cable.
Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
Jimbomakavechi

from United Kingdom

Joined: 11 Aug 2006
Posts: 6
Location: Oxfordshire,
United Kingdom
Thanked: 0 times

PostPosted: Fri Aug 11, 2006 3:18 pm    Post Subject:
Cable size to consumer unit
Reply with quote Thanks

Hi all,
I live in council rented accomodation and the mains cable that feeds the consumer unit seems to be a single core earth cable that is about 6mm to the outer plastic covering. This seems too small to carry all of the mains power. Do you think that this is correct, or could it be dangerous?

Thanks,

Jim
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Pens

from United Kingdom

Joined: 17 Jan 2006
Posts: 2433
Location: Kent,
United Kingdom
Thanked: 0 times

PostPosted: Fri Aug 11, 2006 3:41 pm    Post Subject:
Reply with quote Thanks

I'm not sure why you're asking, is the cable getting hot?
Back to top
 Alert Moderators
Jimbomakavechi

from United Kingdom

Joined: 11 Aug 2006
Posts: 6
Location: Oxfordshire,
United Kingdom
Thanked: 0 times

PostPosted: Fri Aug 11, 2006 3:47 pm    Post Subject:
Reply with quote Thanks

I am asking because typically the councils tradesman do poor quality work and take shortcuts. I am about to buy the flat and once I do any defects are my responsibility, therefore insurance etc could be voided if incorrect or non standard wiring is in place. I would rather get this sorted now if there is a problem rather than have a nasty surprise later.
Back to top
 Alert Moderators
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4541
Location: United Kingdom
Thanked: 10 times

PostPosted: Fri Aug 11, 2006 4:08 pm    Post Subject:
Reply with quote Thanks

Post a picture of the CU area (upload it to some webspace and give use the link) and we will take a look

you should also note that very very few houses are exactly to BS7671, and a large percentage have quite big/lots of defeats, even newbuilds believe it or not (contracts awarded to lowest bidder... who then use cheap unskilled labour, etc) so I wouldn't get too wrapped up in the insurance thing unless your house is a deathtrap electrically wise.

You could have a PIR done if you are worried about your wiring, this can be done by a electrician, however they may not all offer this service
Back to top
 Alert Moderators
Jimbomakavechi

from United Kingdom

Joined: 11 Aug 2006
Posts: 6
Location: Oxfordshire,
United Kingdom
Thanked: 0 times

PostPosted: Fri Aug 11, 2006 4:13 pm    Post Subject:
Reply with quote Thanks

OK will do, thanks. I will also put some appliances on and see if there is any heat actually emanating from the mains feed cable.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Fri Aug 11, 2006 5:29 pm    Post Subject:
Re: Cable size to consumer unit
Reply with quote Thanks

Jimbomakavechi wrote:
Hi all,
I live in council rented accomodation and the mains cable that feeds the consumer unit seems to be a single core earth cable

Just the one? icon_eek.gif

How does that work, then?

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
RMS

from United Kingdom

Joined: 08 May 2006
Posts: 409
Location: United Kingdom
Thanked: 1 time

PostPosted: Fri Aug 11, 2006 7:08 pm    Post Subject:
Reply with quote Thanks

Hope your not getting confused with the earth wire icon_wink.gif
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16491
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Fri Aug 11, 2006 10:08 pm    Post Subject:
Reply with quote Thanks

If it's TT, 6mm2 suffices...

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4541
Location: United Kingdom
Thanked: 10 times

PostPosted: Fri Aug 11, 2006 10:11 pm    Post Subject:
Reply with quote Thanks

securespark wrote:
If it's TT, 6mm2 suffices...


Even if its not... 6mm˛ just scrapes through on the adiabatic IIRC(assuming that the Ze is low enough to clear the service fuse in 5s or less and if its not, you have bigger issues...)
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Sat Aug 12, 2006 8:05 am    Post Subject:
Re: Cable size to consumer unit
Reply with quote Thanks

Jimbomakavechi wrote:

... 6mm to the outer plastic covering. ...


I don't know what that means, but I don't think it means 6mm˛
Back to top
 Alert Moderators
Gaz the Sparky

from United Kingdom

Joined: 16 Mar 2006
Posts: 121
Location: Staffordshire,
United Kingdom
Thanked: 0 times

PostPosted: Sat Aug 12, 2006 8:33 am    Post Subject:
Council Electrics
Reply with quote Thanks

I work for a local city council rewiring and maintaing council houses and the wiring is certainly isnt a bodge. There seems to be this misconception that council workers are ruff and bodge jobs well they dont. My council even go to the lengths of installing 10mm t&e for a cooker circuits (to future proof) where as new builds use 6mm t&e

Right rant over but it does wind me up when people say thay council workers are ruff because I CERTAINLY AM NOT!!!!

icon_evil.gif icon_twisted.gif icon_evil.gif
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Sat Aug 12, 2006 8:41 am    Post Subject:
Reply with quote Thanks

I'd second that, councils tend to think in terms of total cost of ownership so are willing to specify a quality that won't need frequent maintenance and upgrade.

Will buy on specification first and price second.
Back to top
 Alert Moderators
Gaz the Sparky

from United Kingdom

Joined: 16 Mar 2006
Posts: 121
Location: Staffordshire,
United Kingdom
Thanked: 0 times

PostPosted: Sat Aug 12, 2006 9:14 am    Post Subject:
Reply with quote Thanks

Cheers John D nice to know not everyone feels the same way about council workmanship

icon_biggrin.gif icon_biggrin.gif icon_biggrin.gif
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10753
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Sat Aug 12, 2006 6:10 pm    Post Subject:
Reply with quote Thanks

And as for the standard of workmanship, I have worked in countless council wired houses, and it is incredibly rare to find a bad one. I also used to work with a few ex-council sparks, and they was never any bodging or corner cutting going on.
Back to top
 Alert Moderators
RMS

from United Kingdom

Joined: 08 May 2006
Posts: 409
Location: United Kingdom
Thanked: 1 time

PostPosted: Sat Aug 12, 2006 6:29 pm    Post Subject:
Reply with quote Thanks

Have to agree that most council properties are to a high standard.
I test many council houses and find that the standard of work and accessaries used are high quality. Periodic inspection is carried out at change of tenancy so most properties are of a standard that complies to the current wiring regulations and they have to funding/ money to do it the right way and not cut corners.

I know a few people that work for the local council and they are very knowledgable because they get to take up many courses such as ONC/HNC that other companies just would not be able to justify.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
[b]Cable size and type between the meter and consumer unit[/ 3 720 Tue Dec 23, 2003 8:22 pm
Size of amp in consumer unit 7 420 Tue Mar 06, 2007 2:43 pm
Consumer meter tail length and size?. 6 1200 Fri Jun 29, 2007 8:33 pm
New cooker cable size 2 5240 Sat Dec 16, 2006 11:19 am
CABLE SIZE 4 3100 Sat Dec 02, 2006 5:06 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.