lebowski

Joined: 16 Aug 2006 Posts: 3 Location: London, United Kingdom Thanked: 0 times
|
Posted: Wed Aug 16, 2006 8:40 pm Post Subject: Capping cables |
 |
|
I have run my electrical cables in the prescribed zones and have used metal capping,it seems easier to use than plastic.Does all this capping need to be earthed? It will all be buried beneath the plaster. |
|
simon_d

Joined: 30 Apr 2006 Posts: 224 Location: United Kingdom Thanked: 0 times
|
|
Pens

Joined: 17 Jan 2006 Posts: 2433 Location: Kent, United Kingdom Thanked: 0 times
|
Posted: Wed Aug 16, 2006 10:04 pm Post Subject: |
 |
|
For future reference you only need to earth the metal capping if you run it outside of the prescribed zones. |
|
ebee

Joined: 14 Aug 2005 Posts: 1067 Location: Lancashire, United Kingdom Thanked: 0 times
|
Posted: Thu Aug 17, 2006 5:01 am Post Subject: |
 |
|
if you run outside zones then capping not much use anyway.
unless you protecting from plasterers trowel then capping is not much good and metal capping is positively a very bad idea.
Signed
The society against capping cables |
|
simon_d

Joined: 30 Apr 2006 Posts: 224 Location: United Kingdom Thanked: 0 times
|
|
Pens

Joined: 17 Jan 2006 Posts: 2433 Location: Kent, United Kingdom Thanked: 0 times
|
|
simon_d

Joined: 30 Apr 2006 Posts: 224 Location: United Kingdom Thanked: 0 times
|
Posted: Thu Aug 17, 2006 8:59 pm Post Subject: |
 |
|
| Pensdown wrote: | | simon_d wrote: | | Pensdown wrote: | | For future reference you only need to earth the metal capping if you run it outside of the prescribed zones. |
but it should be earthed steel conduit. capping has very little resistance to a drill |
I'm not aware of any regs thats say it has to be steel conduit are you? |
522-06-06 A cable should concealed in a wall or partition at a depth of less than 50mm form the surface of the wall or partition shall:
(i) incorporate an earthed metallic covering which complies with the rewuirements of these regulations for a protective conductor of the circuit concerned, the cable complying with BS 5467, 6346, 6724, 7846, BS EN 60702-1 or BS 8436
now, AFAIK, capping doesnt count as a protective conductor
522-06-06
(iii) be enclosed in earthed conduit, trunking or ducting satisfying the requirements of these regulations....
OK, maybe i was slightly off with the earthed steel conduit, but either way, as far as im aware, capping doesnt comply |
|
Pens

Joined: 17 Jan 2006 Posts: 2433 Location: Kent, United Kingdom Thanked: 0 times
|
Posted: Thu Aug 17, 2006 9:09 pm Post Subject: |
 |
|
Although it's far from ideal, earthed metal capping does comply with 7671. You can't use it where the cable is less than 50mm from both sides but on a normal block wall it can be used. |
|