new hob

This topic originated from the How to page called Choosing the correct size cable
Click here to return to the page called Choosing the correct size cable.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
WAVYdavy

from United Kingdom

Joined: 18 Aug 2006
Posts: 3
Location: Northumberland,
United Kingdom
Thanked: 0 times

PostPosted: Fri Aug 18, 2006 7:40 pm    Post Subject:
new hob
Reply with quote Thanks

just bought a De Dietrich hob, the DTI304, i won't be installing it myself however, i'm confused about the wiring, it is supplied, fitted, with a 1.5mm wire which consists of one blue & one brown which are connected together a metal tab which are identified in the book as neutral, two black wires which are connected together a metal tab which are identified in the book as phase and one single wire green/yellow, this is the only one i understand! as this hob is rated as 5.9kw why is a 1.5mm fitted? also the book seems to suggest "plugging it in", surely this can't be right. any help would be appreciated. icon_question.gif
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
fireman22

from United Kingdom

Joined: 18 Mar 2005
Posts: 605
Location: United Kingdom
Thanked: 0 times

PostPosted: Fri Aug 18, 2006 8:03 pm    Post Subject:
Reply with quote Thanks

did it come with this 1.5mm cable attached, it wasn't just on to test the unit.
1.5mm flex is rated at 16 amps or so, therefore it will not take 5.9 KW unless the element are interlocked so that only some can be on at the same time and therefore wont take over 3 KW at any one time. have you got the installation book you could scan and post?
Back to top
 Alert Moderators
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4538
Location: United Kingdom
Thanked: 10 times

PostPosted: Fri Aug 18, 2006 8:19 pm    Post Subject:
Reply with quote Thanks

Sounds like a three phase hob...

(that may or may not have been rather badly converted to SP [your post isn't exactly that easy to follow])
Back to top
 Alert Moderators
WAVYdavy

from United Kingdom

Joined: 18 Aug 2006
Posts: 3
Location: Northumberland,
United Kingdom
Thanked: 0 times

PostPosted: Fri Aug 18, 2006 8:52 pm    Post Subject:
Reply with quote Thanks

thanx guys, in answer to your points, i bought this from john lewis this morning brand new with the wire attached. the booklet only shows wiring as explained in first letter. there is a three phase wiring instruction in the book in which the black wires are split for phase one & phase 2 the blue & brown stay together and go to neutral and yellow/green goes to earth. i thought tha the flex is under rated. in the book it has the following info:
220-240 V monophase
fuse:32/16amp

thanx for you help guys
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16480
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Fri Aug 18, 2006 11:06 pm    Post Subject:
Reply with quote Thanks

monophase sounds right. But there's a big difference between 32 and 16A!!

5.9 = nearly 26A. So 2.5 minimum.

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
WAVYdavy

from United Kingdom

Joined: 18 Aug 2006
Posts: 3
Location: Northumberland,
United Kingdom
Thanked: 0 times

PostPosted: Sat Aug 19, 2006 7:51 am    Post Subject:
hob
Reply with quote Thanks

i agree "there's a big difference between 32 and 16A!!" even if the sparks connects 2.5mm from the switch to the cu i still see the fitted 1.5mm as a weak link and possible fire risk? does it have any baring that this hob is an induction type?
Back to top
 Alert Moderators
knowalittle

from United Kingdom

Joined: 04 Feb 2007
Posts: 7
Location: Middlesex,
United Kingdom
Thanked: 0 times

PostPosted: Tue Feb 06, 2007 9:04 am    Post Subject:
Reply with quote Thanks

Hi WavyDavy !

I juts bought the same hob, what did you end up doing with the cable situation?
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12845
Location: Yorkshire,
United Kingdom
Thanked: 21 times

PostPosted: Tue Feb 06, 2007 9:12 pm    Post Subject:
Reply with quote Thanks

No good asking WavyDavy. He made 3 posts in August last year as a DIYer wanting help. Chances are, he probably will never come to this forum again.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.