Air pressure switch

B

Bamber gaspipe

Does ANYBODY,ANYWHERE,know how to test an air pressure switch using a multimeter...Worcester Greenstar 24i junior..apart from the usual k*nob heads who will obviously ignore can anyone give a definitive answer?...your input most appreciated.
 
Sponsored Links
here goes then ,hope you are a competent class to do this ..


with the power to the boiler off,

remove the air pressure switch
connector on the pcb ,

It is a 4 pin molex connector on the fuelsaver,
with 3 wires coming out.
You should be able to check which is the
normally closed, common and normally open from looking for the
corresponding colour wires on the microswitch on the APS.
Using a multimeter (checking the lead resistance by touching them together),
look for less than an ohm resistance between the normally closed and
common on the molex connector.
Doing it this way will also check out
the wiring to the APs as well as the pressure switch itself

The aps body should have one or two rubber hoses connected to it.

Pull the other end of the tube off so you can activate the APS by sucking or
blowing. Depending on which tube, either suck or blow GENTLY to activate
the microswitch and test the common to normally open contacts on the
molex connector, again this should be less than an ohm.
 
Bamber gaspipe said:
Does ANYBODY,ANYWHERE,know how to test an air pressure switch using a multimeter...Worcester Greenstar 24i junior..apart from the usual k*nob heads who will obviously ignore can anyone give a definitive answer?...your input most appreciated.

Bamber.

Try this site for your little problem ;)



http://www.angermanage.co.uk/
 
Moz said:
It is a 4 pin molex connector on the fuelsaver,
with 3 wires coming out.
You should be able to check which is the
normally closed, common and normally open from looking for the
corresponding colour wires on the microswitch on the APS.
Using a multimeter (checking the lead resistance by touching them together),
look for less than an ohm resistance between the normally closed and
common on the molex connector.
Doing it this way will also check out
the wiring to the APs as well as the pressure switch itself

The aps body should have one or two rubber hoses connected to it.

Pull the other end of the tube off so you can activate the APS by sucking or
blowing. Depending on which tube, either suck or blow GENTLY to activate
the microswitch and test the common to normally open contacts on the
molex connector, again this should be less than an ohm.



Awesome.. Thanx Moz, I have understood every word that you have said,will try this tomorrow (although problem is solved)...Nice to see someone getting to the point instead of the usual dancing around the fact ``that they do not know `` routine..How bleedin` straightforward was that?? Will post back & let you know how I get on..many thanks again.. ;) ;) ;) (Hope it works) :LOL:
 
Sponsored Links
scatmanjohn said:
Bamber gaspipe said:
Does ANYBODY,ANYWHERE,know how to test an air pressure switch using a multimeter...Worcester Greenstar 24i junior..apart from the usual k*nob heads who will obviously ignore can anyone give a definitive answer?...your input most appreciated.

Bamber.

Try this site for your little problem ;)



http://www.angermanage.co.uk/


Very clever, although I do not understand why you think I am angry :rolleyes:
 
I always expected to end up like that Steve Coogan charactor "Saxondale "in anger management classes ..lol ;)
 
Scatman ...I am not angry...you are a lovely person & I would love to be your best friend..How about it....(big scary cheesey grin) :evil:
 
Bamber gaspipe said:
Scatman ...I am not angry...you are a lovely person & I would love to be your best friend..How about it....(big scary cheesy grin) :evil:

I see you have visited the site that i suggested. :LOL:

Keep at it, being able to talk about it is half the battle. :LOL:

If, in one of your dark moments, you find yourself posting the odd profanity just think of me or visit the afor mentioned interweb site.

Good Luck :LOL: :LOL:
 
Scatman`s a shirtlifter...uphill gardener..wotchit Moz... :eek:
 
not worked on this boiler but, does the condens sensor have to make after the aps but before ignition process.
 
Bamber gaspipe said:
Scatman`s a shirtlifter...uphill gardener..wotchit Moz... :eek:

Homophobe

Which means:

n. One with an irrational fear of homosexuality and homosexuals. For the most part these people seem to have little actual experience with the aforementioned.

We fear what we do not understand.

I can't have my boyfriend over because my parents are total homophobes.

I'm arranging a outing to G.A.Y in London are you interested
 
Absolutely..do I have to wear ill fitting pants & mince about...hope so..Who`s Fitz talking to?.
 