Moving light switch to the other side of the door

Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
mp01

from United Kingdom

Joined: 25 Aug 2006
Posts: 11
Location: United Kingdom

PostPosted: Thu Sep 07, 2006 7:26 pm Reply with quote

I'm changing my door to open the opposite way and want to change my light switch to suit. Is it ok to put a junction box where the old switch is and run a new flex to the new location? The current flex isn't long enough to reach the new location.

I know I should probably replace the exsisting flex with a new/longer flex to the new location, however this isnt ideal because the flex goes up into the ceiling, which I'm not too fond of the idea of tearing up the ceiling and having it replastered again. I also can't access it from above as there's another flat and it would require their laminate floors being removed and then the floor boards under that.

By moving the switch to the other side via a junction, do I need to have an electrical certificate or is it notifiable to my local building reg? From what I understand according to Part P of the Building Regs, I don't need to notify building regs, but I'm not sure if I need to have an electric cert? I seem to recall reading something previously as of Jan 2005 most electrical work needs to have a certificate?
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
industryspark

from United Kingdom

Joined: 08 Jul 2006
Posts: 616
Location: Yorkshire,
United Kingdom
Thanked: 8 times

PostPosted: Thu Sep 07, 2006 7:41 pm Reply with quote

Quote:
I'm changing my door to open the opposite way and want to change my light switch to suit.


is this really necessary?

Quote:
Is it ok to put a junction box where the old switch is and run a new flex to the new location?


this would look very ugly if ive got the picture of what your wanting to do right in my head?
a junction box would be allowable, are you on about surface wiring the new light switch.....if so then it will need some protection in the form of conduit/ trunking.

Quote:
flex


do you mean cable, as in twin and earth?

a flex is what is on an appliance, tv, radio, ect.

Quote:
By moving the switch to the other side via a junction, do I need to have an electrical certificate or is it notifiable to my local building reg?


not sure on this one as its not a new circuit as such but not exactly a straight forward replacement either. id say no to be honest but check this out.



i think a minor works certificate would be required here[/quote]
Back to top
 Alert Moderators
mp01

from United Kingdom

Joined: 25 Aug 2006
Posts: 11
Location: United Kingdom

PostPosted: Thu Sep 07, 2006 8:19 pm Reply with quote

Quote:
Quote:
I'm changing my door to open the opposite way and want to change my light switch to suit.


is this really necessary?


yes, otherwise you won't be able to turn the light on. The door is being changed to open towards the wall rather then to the middle of the room.

Quote:
flex?

I meant the cable for the lights - sorry

Quote:
Quote:
Is it ok to put a junction box where the old switch is and run a new flex to the new location?


this would look very ugly if ive got the picture of what your wanting to do right in my head?


No this won't be surface mounted. I want to put the junction box where the current electrical mounting box is, then run the cable from it to the door, then run it along the door support/frame (under the facing) then from under the facing to the new mounting box on the other side. The junction box will be plastered over. The cables will be shielded and plastered over except where they run along the door support under the facing.
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 15977
Location: Yorkshire,
United Kingdom
Thanked: 225 times

PostPosted: Thu Sep 07, 2006 8:30 pm Reply with quote

mp01 wrote:
The junction box will be plastered over.


NO IT WILL NOT. icon_evil.gif icon_evil.gif icon_evil.gif icon_evil.gif icon_evil.gif

get that idea out of your head RIGHT NOW.
Back to top
 Alert Moderators
mp01

from United Kingdom

Joined: 25 Aug 2006
Posts: 11
Location: United Kingdom

PostPosted: Thu Sep 07, 2006 8:40 pm Reply with quote

I'll take your word for it, because you guys know more then I do, but can just ask why? How else can I discretely extend the cable?
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 17659
Location: Leeds,
United Kingdom
Thanked: 970 times

PostPosted: Thu Sep 07, 2006 8:59 pm Reply with quote

You could replace the existing switch with a blanking plate and join the wires behind this. (but not plaster over it)

Or you could replace the switch cable from the ceiling rose, and extend it to the position of the new switch.

As for why, any screwed connection must be accesible for inspection and testing as the screws can work lose over time.
Back to top
 Alert Moderators
mp01

from United Kingdom

Joined: 25 Aug 2006
Posts: 11
Location: United Kingdom

PostPosted: Thu Sep 07, 2006 9:10 pm Reply with quote

hmm... I did think about the blanking plate but didnt like the look.

Can't really replace the cable from the ceiling rose, as I would have to dig the cable out of the plaster along the wall to the ceiling (all the cables have been plastered into the walls unprotected - not by me but the council) then dig through the coving then the coat of plaster on the ceiling then through 2 boards of plaster boards just to get to it. Can't get to from the top as I would have to remove my neighbors laminate floors then their floor boards to get to it. So it's not exactly ideal to replace the cable.

Why can't the junction box be plastered over? Is it because the wire becomes hidden? Or is it because the plaster is wet and if that is the case then could a piece board/wood go over the box before plastering?
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 17659
Location: Leeds,
United Kingdom
Thanked: 970 times

PostPosted: Thu Sep 07, 2006 9:14 pm Reply with quote

mp01 wrote:
Why can't the junction box be plastered over? Is it because the wire becomes hidden? Or is it because the plaster is wet and if that is the case then could a piece board/wood go over the box before plastering?


RF Lighting wrote:
As for why, any screwed connection must be accesible for inspection and testing as the screws can work loose over time.
Back to top
 Alert Moderators
mp01

from United Kingdom

Joined: 25 Aug 2006
Posts: 11
Location: United Kingdom

PostPosted: Thu Sep 07, 2006 9:23 pm Reply with quote

oh... blanking plate it is then.
cheers
Back to top
 Alert Moderators
mp01

from United Kingdom

Joined: 25 Aug 2006
Posts: 11
Location: United Kingdom

PostPosted: Thu Sep 07, 2006 9:27 pm Reply with quote

Just thought of something.... the lighting junction box is in the ceiling and it has screw terminals and it's not exactly accessible to check. icon_question.gif
Back to top
 Alert Moderators
mp01

from United Kingdom

Joined: 25 Aug 2006
Posts: 11
Location: United Kingdom

PostPosted: Thu Sep 07, 2006 10:04 pm Reply with quote

Ok, I answered my own question.....

"Junction boxes must be fixed solidly to a firm, suitable surface and must be accessible. This does not mean they have to be visible and can be fixed in floor or roof voids. Accessible means to a builder or electrician who can easily remove part of the floor or ceiling etc. Junction boxes may not be buried in plaster."

http://www.diydoctor.org.uk/projects/junctionbox.htm

Although, my ceiling isnt exactly accessible with a layer of plaster then 2 layers of plaster boards icon_confused.gif
Back to top
 Alert Moderators
Pens

from United Kingdom

Joined: 17 Jan 2006
Posts: 2437
Location: Kent,
United Kingdom
Thanked: 2 times

PostPosted: Thu Sep 07, 2006 10:27 pm Reply with quote

mp01 wrote:
Ok, I answered my own question.....

"Junction boxes must be fixed solidly to a firm, suitable surface and must be accessible.

There are no regulations that say JB's must be fixed or accessible. It is very good practice to do both but under some circumstances by fixing JB's they become inaccessible ie above down lighters in ground floor ceilings

Mr diydoctor has lead you astray icon_wink.gif
Back to top
 Alert Moderators
mp01

from United Kingdom

Joined: 25 Aug 2006
Posts: 11
Location: United Kingdom

PostPosted: Fri Sep 08, 2006 8:32 am Reply with quote

oohh...

So then it's ok to plaster over the junction box and it is legal, it's just not normal practice?

I spent half the night trying to find anything in the regulations regarding this and didn't find any.....
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 25275
Location: Cheshire,
United Kingdom
Thanked: 445 times

PostPosted: Fri Sep 08, 2006 3:59 pm Reply with quote

NO!

You cannot plaster over a junction box!

Screwed connections need to remain accessible!

You could, however invest in some good quality crimpers and terminals and join the conductors this way, sleeving them in heatshrink so they are insulated to 240V. THEN you could plaster over them.
Back to top
 Alert Moderators
mp01

from United Kingdom

Joined: 25 Aug 2006
Posts: 11
Location: United Kingdom

PostPosted: Fri Sep 08, 2006 4:20 pm Reply with quote

I phoned my local council to find out if moving the light switch is notifiable or requires an electrical certificate..... I was told it must be done by a qualified electrician and a certificate is needed. She didn't clarify that it was notifiable. She also stated that changing a single socket to a double or changing a light fixture doesn't require a certificate, however everything else does including moving or extending wires. This seems to contradict what I've read with Part P.

Can't really say how qualified she was in the field as it was the receptionist that I spoke to. I had asked to speak to someone regarding electrical regulations and she wanted to know what the question was and then said that.

But anyways, I think I have found the best solution... I found a 1 Gang Arctitrave Blank Plate which is 31mm in width (it was suggested earlier to use a blank plate)... There is space under the top door facing of 40mm wide from the top of the door wood frame to the top of the facing.

I'll install a new box and the plate there and put the facing over it - keeping it accessible and out of view icon_biggrin.gif

I've never used a blanking plate and I've tried looking for a wiring diagram online but haven't found one yet....

RF Lighting said
Quote:
You could replace the existing switch with a blanking plate and join the wires behind this. (but not plaster over it)


Am I to assume that I wire both cables into the the blank plate? What do you mean by joining the wires behind this?
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Moving light switch from one side of a door to another 9 1900 Mon May 09, 2005 4:20 pm
Light switch on hinge side of door... 12 920 Thu Mar 01, 2007 9:34 pm
Installing an out side pir light by back door 4 900 Fri Mar 28, 2008 6:17 pm
Relocating a socket to the other side of a door 3 600 Tue Jun 28, 2005 8:57 am
Moving Cooker & Oven to the opposite side of the kitchen 15 220 Tue Dec 03, 2013 11:01 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.