Posted: Tue Sep 12, 2006 2:04 pm Post Subject: shower switch |
 |
|
I am fitting a 10.5kw shower and am using 10mm twin & earth.I am going to put in a 50A MCB and consumer unit already has a 30mA RCD.I will also fit a double pole neon switch outside the bathroom and just need to know if this has to be 50A as well or can I use a 45A? CAble run is only 12 metres max. |
|
securespark

Joined: 11 Jan 2004 Posts: 16480 Location: Cheshire, United Kingdom Thanked: 14 times
|
Posted: Tue Sep 12, 2006 2:53 pm Post Subject: |
 |
|
Best to match or exceed MCB rating. __________________ As George Michael once said, "..if you're gonna do it, do it right, right?" |
|
JohnD

Joined: 15 Nov 2005 Posts: 24037 Location: Hampshire, United Kingdom Thanked: 54 times
|
Posted: Tue Sep 12, 2006 3:11 pm Post Subject: |
 |
|
And double-check the tightness of the terminals holding the wires - especially the Neutral - a few hours after you think you've tightened them, or the next day. |
|
rugbyjunkie

Joined: 08 Apr 2006 Posts: 8 Location: Lanarkshire, United Kingdom Thanked: 0 times
|
Posted: Tue Sep 12, 2006 4:28 pm Post Subject: |
 |
|
Cheers guys |
|