PostPosted: Wed Sep 13, 2006 12:20 pm Reply with quote

Just a quick question, when installing a 3 phase balanced motor (no neutral) Is there anyway to do an Earth Fault Loop Impedance test? Or is the only way by calculation after measuring the External loop, and R1R2.
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Lectrician

from United Kingdom

Joined: 18 Jul 2004
Posts: 7583
Location: Devon,
United Kingdom
Thanked: 291 times

PostPosted: Wed Sep 13, 2006 4:32 pm Reply with quote

If you have a two prong EFL tester, one to live, on to earth.

If it is a 3 prong tester, put the neutral on the earth, and the earth on the earth, and the live to the live.

BE AWARE that if the motor is not actually earthed (this is why you are testing), that it will rise to mains voltage when you stick the live on, as the neutral has 'no where' to go.
Back to top
 Alert Moderators
Maxxy

from United Kingdom

Joined: 10 Sep 2006
Posts: 390
Location: Essex,
United Kingdom

PostPosted: Wed Sep 13, 2006 5:34 pm Reply with quote

Thanks for the quick response. The motor is fully earthed, both by the outer sheath, and a cable inside the armoured cable feeding it.

Its a 3 prong Kewtech tester that ive got. With the method you described, it would be too dangerous, so ill have to stick to calculated readings.

Thanks again
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 17595
Location: Leeds,
United Kingdom
Thanked: 951 times

PostPosted: Wed Sep 13, 2006 7:03 pm Reply with quote

[quote="Maxxy"]The motor is fully earthed,


Maxxy wrote:
With the method you described, it would be too dangerous


Why? If the motor is fully earthed then there will be no problem. If the motor is not earthed then it will rise to mains potential, but your tester will show this.

If you like, for piece of mind you could carry out an ELV continuity test between the earth at the motor and its source before proceding with the EFLI test.
Back to top
 Alert Moderators
Maxxy

from United Kingdom

Joined: 10 Sep 2006
Posts: 390
Location: Essex,
United Kingdom

PostPosted: Wed Sep 13, 2006 7:33 pm Reply with quote

Wouldnt attaching the Neutral and Earth probes to the Earth cable send 230v down the Earth for the duration of the test?

The motor is part of an industrial fan, so a lot of metal work around it where we fix it to the roof - which i would be kneeling on when doing the test.
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 17595
Location: Leeds,
United Kingdom
Thanked: 951 times

PostPosted: Wed Sep 13, 2006 7:42 pm Reply with quote

Yes the tester will 'send 230V down the earth' but it will onlt be a few mA.

Providing there is an earth connected to the motor then the metal work will not come live.

Attaching your tester in this way in no more dangerous that carring out an ELFI test using three test leads.
Back to top
 Alert Moderators
Maxxy

from United Kingdom

Joined: 10 Sep 2006
Posts: 390
Location: Essex,
United Kingdom

PostPosted: Wed Sep 13, 2006 8:04 pm Reply with quote

Brilliant, thanks alot for clearing that up for me
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Bridging between Phase and CPC etc when testing 13 1660 Fri Dec 21, 2007 3:47 pm
Three phase testing 3 2380 Fri Jun 30, 2006 6:03 pm
3 phase testing 21 5360 Sat May 14, 2005 2:26 pm
PAT testing 3 phase 12 380 Sat Oct 08, 2011 8:30 pm
Testing a three phase supply 8 280 Sat Dec 15, 2012 11:47 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.