:( My boiler has started running for no reason for a few seconds several times a day I have also noticed it continues running a short duration when I have turned off the hot tap I at a loss it feels expensive any help appreciated MIKEL
 
Sponsored Links
mikel12 said:
:( My boiler has started running for no reason for a few seconds several times a day I have also noticed it continues running a short duration when I have turned off the hot tap I at a loss it feels expensive any help appreciated MIKEL

crystal%20ball.jpg


read this
 
Its an Ideal Mini, or a Biasi or a Halstead and the DHW flow switch gland is leaking and sticking and the switch is turning on the hot water when its not required but it goes to the rads as the diverter is in the heating position.

It might also a Puma but I dont think so.

Tony
 
Or a turbomax or similar which has got its keep-me-hot turned on for the first time.
 