PostPosted: Fri Sep 22, 2006 9:24 am    Post Subject:
Faulty socket spur
Reply with quote Thanks

My sister had a fualty socket in her kitchen which intermitantly stopped working and then would start working again. The fauty socket ran off as a spur from an upstairs socket, upon investigation I found that the live conductor connection on the upstairs socket that ran to the faulty socket had soot on it.
I checked the no load voltage at the faulty socket and it showed 70v, but any load applied would drop it down to 0v. I assume the 70v is coz of the bad connection on the live conductor due to soot.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
didthathurt

from United Kingdom

Joined: 19 Aug 2006
Posts: 311
Location: Kent,
United Kingdom
Thanked: 0 times

PostPosted: Fri Sep 22, 2006 7:20 pm    Post Subject:
Reply with quote Thanks

If, by the no load voltage, you mean that the voltage at the socket, between the Live and Neutral is 70V without anything plugged in then yes, you do have a problem. You should get a reading of between 220V and 250V (on a British Standard day). The sooting - probably due to a loose connection - could affect the connection between the live supply and the socket by increasing the resistance across that connection and causing a voltage drop (of, in your case, 160V across that connection). That's bad news and I'd expect that fitting to be getting hot. You must rectify this asap. Change the socket and strip the wire back a little to use new clean wire in the connections. Have a good look at the wire and make sure it has not suffered from the heat. Ideally, I think the insulation should be checked using a proper insulation tester.

__________________
Being a professional doesn't mean I'm any good - just that I get paid for doing it!
Back to top
 Alert Moderators
tilla tech

from United Kingdom

Joined: 19 May 2006
Posts: 29
Location: Bedfordshire,
United Kingdom
Thanked: 0 times

PostPosted: Sun Sep 24, 2006 7:07 pm    Post Subject:
Reply with quote Thanks

Done what you mentioned. Works ok.
I couldnt work out where the 70V came from, but the soot thing explains it.

Thanks
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Fused spur faulty? 5 220 Sat Jan 10, 2009 12:55 pm
Faulty socket or dodgy computer? 10 560 Thu Nov 17, 2005 11:01 pm
Shaver socket - faulty? 10 460 Fri Feb 20, 2009 8:43 pm
Faulty wall socket... 3 460 Mon Feb 21, 2005 9:06 am
Faulty Socket ? 4 1500 Mon Jan 09, 2006 10:30 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.