spurs

This topic originated from the How to page called Adding a spur to a ring circuit from a junction box
Click here to return to the page called Adding a spur to a ring circuit from a junction box.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
johnphillips

from United Kingdom

Joined: 09 Oct 2006
Posts: 3
Location: Cambridgeshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 09, 2006 9:49 am    Post Subject:
spurs
Reply with quote Thanks

If a junction box is installed in the ring circuit(power) and a FSU run from this (5A in this case), can another FSU be wired in to this junction box? or must another box be wired into the ring? This is not a spur from a spur but just two FSU supplies running into one box.

thanks John
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Pens

from United Kingdom

Joined: 17 Jan 2006
Posts: 2433
Location: Kent,
United Kingdom
Thanked: 0 times

PostPosted: Mon Oct 09, 2006 6:24 pm    Post Subject:
Reply with quote Thanks

Yes, you can do that if you wish but make sure the JB is accessible and to keep with convention the cable feeding the FCU's should be 2.5 T&E.

If you're using the new colours you should also label your consumer unit to say that. You can get stickers when you buy you cable etc.
Back to top
 Alert Moderators
johnphillips

from United Kingdom

Joined: 09 Oct 2006
Posts: 3
Location: Cambridgeshire,
United Kingdom
Thanked: 0 times

PostPosted: Wed Oct 11, 2006 12:12 pm    Post Subject:
spurs
Reply with quote Thanks

Pensdown wrote:
Yes, you can do that if you wish but make sure the JB is accessible and to keep with convention the cable feeding the FCU's should be 2.5 T&E.

If you're using the new colours you should also label your consumer unit to say that. You can get stickers when you buy you cable etc.


Thanks for that Pensdown, I am still confused, the condensed IEE comments are that only one spur may be wired from a socket in a ring why is this different from a JB, also on the blurb on a 30A JB from a well known DIY retailer it says "WARNING" only one socket or spur may be wired into this junction box! it gives a small diagram illustrating one socket/spur wired from the ring ! any ideas ?
Back to top
 Alert Moderators
didthathurt

from United Kingdom

Joined: 19 Aug 2006
Posts: 311
Location: Kent,
United Kingdom
Thanked: 0 times

PostPosted: Wed Oct 11, 2006 1:08 pm    Post Subject:
Reply with quote Thanks

The well known DIY retailer is covering itself against a single cable powering multiple unfused spurs being run from the JB. If you are wiring 2 seperate spurs into the JB, you could argue that there is an infinitessimally small length of the ring main connecting the 2. What you are proposing will not exceed the max load of the 30Amp JB because the fuses in the FSU's will limit the current drawn by each of the spurs. I would see no problem in doing as you propose with the normal accessibility and Part P caveats.

__________________
Being a professional doesn't mean I'm any good - just that I get paid for doing it!
Back to top
 Alert Moderators
Paul Barker

from United Kingdom

Joined: 04 Aug 2005
Posts: 5481
Location: Yorkshire,
United Kingdom
Thanked: 18 times

PostPosted: Wed Oct 11, 2006 3:53 pm    Post Subject:
Reply with quote Thanks

My only additional thought, and I am sure you have this covered, is that a socket on a ring can only supply one spur because sockets are designed to take a maximum of 3 cables.

Now if you say that a 30 amp JB is designed for four I will believe you because I know no better, if not then OP will have to use a higher rating JB to accomodate the extra.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16480
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Wed Oct 11, 2006 7:07 pm    Post Subject:
Reply with quote Thanks

Why not extend the ring?

You are fitting two new cables, which would be the same if you extended the ring.

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12845
Location: Yorkshire,
United Kingdom
Thanked: 21 times

PostPosted: Wed Oct 11, 2006 8:12 pm    Post Subject:
Reply with quote Thanks

securespark wrote:
Why not extend the ring?

You are fitting two new cables, which would be the same if you extended the ring.

Perhaps one cable is going up, the other down?
Back to top
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 4932
Location: Oxfordshire,
United Kingdom
Thanked: 63 times

PostPosted: Wed Oct 11, 2006 9:27 pm    Post Subject:
Reply with quote Thanks

Ooh great, could I then get a nice big Henley block, pop it on my ring circuit and patch in 10 spurs off the one junction? I don't think so....

TTC
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Wed Oct 11, 2006 10:00 pm    Post Subject:
Reply with quote Thanks

good question, as always you have to think about ring balance but two JBs close together is not signifianctly different from one JB with multiple spurs and the latter is neater and less prone to failure (every connection is a potential point of failure so minimise the number)

lots of load concentrated close together on a ring and not near the center is a bad thing regardless of if that load comes from a load of spurs in one JB, a load of spurs coming off multiple sources close togehter a load of sockets close together running lots of equipment.
Back to top
 Alert Moderators
johnphillips

from United Kingdom

Joined: 09 Oct 2006
Posts: 3
Location: Cambridgeshire,
United Kingdom
Thanked: 0 times

PostPosted: Thu Oct 12, 2006 8:23 am    Post Subject:
Reply with quote Thanks

securespark wrote:
Why not extend the ring?

You are fitting two new cables, which would be the same if you extended the ring.

No, this is impractical since the two FSU's are in completly different areas.
The only way of doing it this way would be to wire the FSU's into the ring and run the spurs out from these, since the ring is in the loft and one of the FSU's is switched this is again impractical.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Spurs 2 240 Fri Dec 14, 2007 9:35 pm
Ring main and spurs 4 500 Tue Dec 04, 2007 11:08 pm
sockets are all spurs!!? 5 500 Sun Dec 02, 2007 1:16 am
Can fused spurs be put in series 10 640 Sat Nov 03, 2007 7:09 am
Switched spurs for the gamesroom 4 200 Tue Feb 05, 2008 12:18 am