Posted: Wed Oct 18, 2006 10:51 am Post Subject: Similar to mains or lighting ring? |
 |
|
I have installed security lights before on my garage and used the small fuse box/cu to take a feed off the internal garage light supply. Now I want to install a 150w security light on the house. Is it ok to do so using the appropriate 3 core flex but terminate it in a plug that is 5amp supplied and then plug it into the internal wall power supply socket? It would appear messy to me to try and terminate it at the mains circuit breaker box in the study? Thanks.. |
|
didthathurt

Joined: 19 Aug 2006 Posts: 311 Location: Kent, United Kingdom Thanked: 0 times
|
Posted: Wed Oct 18, 2006 1:23 pm Post Subject: |
 |
|
Yes, it is OK but messy, as you say. 5Amps is too much, though. A 3 Amp fuse would be more than adequate (150W only draws 2/3 of an Amp!). __________________ Being a professional doesn't mean I'm any good - just that I get paid for doing it! |
|