ELECTRIC FULLY TRIPPING OUT - please help!

This topic originated from the How to page called Identifying a faulty circuit
Click here to return to the page called Identifying a faulty circuit.
Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
Search this topic :: View previous topic :: View next topic  
Author Message
cashka76

from United Kingdom

Joined: 26 Oct 2006
Posts: 1
Location: Warwickshire,
United Kingdom

PostPosted: Thu Oct 26, 2006 11:18 am Reply with quote

Hope you can help. Our Hager consumer unit is tripping out intermittently (maybe about once a day). It is the MAIN switch that goes, not just one of the individual fuses, so we are really stumped as to where the problem could be. I have noticed over the last week that it tends to happen at about 6.30 in the morning!!! Is it possible that there is some kind of incoming surge in power at that time that results in the whole thing blowing?

Hope you can help shed some light!

Claire
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
Inky Pete

from United Kingdom

Joined: 24 Oct 2006
Posts: 607
Location: Cheshire,
United Kingdom
Thanked: 43 times

PostPosted: Thu Oct 26, 2006 11:27 am Reply with quote

The problem's going to be something internal to the house, not any kind of incoming surge.

What time does your heating come on in the morning?
Back to top
 Alert Moderators
slippyr4

from United Kingdom

Joined: 12 Jul 2005
Posts: 775
Location: Bedfordshire,
United Kingdom
Thanked: 4 times

PostPosted: Thu Oct 26, 2006 4:18 pm Reply with quote

is your "main switch" actually an RCD? with a test button, and something like 60A/30mA written on it?

A isolator switch will not turn itself off unless you have poltergeists.
Back to top
 Alert Moderators
industryspark

from United Kingdom

Joined: 08 Jul 2006
Posts: 616
Location: Yorkshire,
United Kingdom
Thanked: 8 times

PostPosted: Thu Oct 26, 2006 4:49 pm Reply with quote

im thinking the post is reffering to an RCD.

if it happens consistently at the same time then the fault should be easy to find.

once you think you know the offending circuit, you could leave that circuit off for a few days running to see if that is indeed the problem.
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 15977
Location: Yorkshire,
United Kingdom
Thanked: 225 times

PostPosted: Thu Oct 26, 2006 6:32 pm Reply with quote

Definitely an RCD. What sort of earth system do you have? Unless its TT, with an earth rod, theres no need for the mainswitch to be an RCD (and it shouldn't be, for the reason you've highlighted in your post - all the electric goes off it theres a fault). An electrician could alter this setup for you. I reckon your heating is set to come on at 6:30 icon_wink.gif
Back to top
 Alert Moderators
Markir

from United Kingdom

Joined: 03 Dec 2006
Posts: 4
Location: Surrey,
United Kingdom

PostPosted: Sun Dec 03, 2006 8:01 pm Reply with quote

_____________________________
lynda, moderator

please note forum rule 20
Back to top
 Alert Moderators
chrisbyrd

from United Kingdom

Joined: 08 Oct 2006
Posts: 120
Location: Cambridgeshire,
United Kingdom

PostPosted: Sun Dec 03, 2006 8:04 pm Reply with quote

does anything else come on at 6.30? anyone getting up early for a shower?
Back to top
 Alert Moderators
Big_Spark

from United Kingdom

Joined: 20 Feb 2004
Posts: 3434
Location: United Kingdom
Thanked: 1 time

PostPosted: Sun Dec 03, 2006 8:40 pm Reply with quote

cashka76 wrote:
Hope you can help. Our Hager consumer unit is tripping out intermittently (maybe about once a day). It is the MAIN switch that goes, not just one of the individual fuses, so we are really stumped as to where the problem could be. I have noticed over the last week that it tends to happen at about 6.30 in the morning!!! Is it possible that there is some kind of incoming surge in power at that time that results in the whole thing blowing?

Hope you can help shed some light!

Claire


Claire, check the timer settings for your heating system or water heating system (Immersion), whichever you have. It could be that one of the parts of this system has developed a fault and is causing the trip.

Also, what time do you and your partner rise in the morning? Is there something about your routine that could shed some light on the matter? Do you have an electric or power shower that is invariably used at about 06:30?

Have a good think, it is likely to be something simple to identify when you check everything.
Back to top
 Alert Moderators
Invisible-Man

from United Kingdom

Joined: 25 Mar 2006
Posts: 315
Location: Essex,
United Kingdom

PostPosted: Sun Dec 03, 2006 9:25 pm Reply with quote

Am I right in thinking that if you were to detect the circuit of the fault (so happens to be a neutral/earth fault), then isolate via keeping mcb switched off on that circuit the fault would still trip a RCD !!!
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 25246
Location: Cheshire,
United Kingdom
Thanked: 445 times

PostPosted: Sun Dec 03, 2006 9:34 pm Reply with quote

If it's an N/E fault, yes. If an L/E fault, it is possible to isolate it by switching mcb off.
Back to top
 Alert Moderators
ricicle

from United Kingdom

Joined: 14 Sep 2006
Posts: 6308
Location: Gloucestershire,
United Kingdom
Thanked: 377 times

PostPosted: Sun Dec 03, 2006 9:36 pm Reply with quote

Neutral/earth fault can trip RCD with its Phase conductor isolated - it depends if there are any other circuits drawing current giving rise to imbalance in the RCD because of their neutral current leaking to earth via the fault
Back to top
 Alert Moderators
Invisible-Man

from United Kingdom

Joined: 25 Mar 2006
Posts: 315
Location: Essex,
United Kingdom

PostPosted: Sun Dec 03, 2006 9:47 pm Reply with quote

securespark wrote:
If it's an N/E fault, yes. If an L/E fault, it is possible to isolate it by switching mcb off.


The point I was getting to, is that to completely isolate a found fault (neutral/earth) not knowing the reason for it and not a plugged in item, you would have to say in a immersion heater physically un-wire the heater to stop the RCD from tripping rather than switching the MCB off, maybe a difficult task for a DIY'er, and could make tracking down a fault a bit more difficult than just isolating a circuit by switching MCB's off one by one, thus throwing a DIY'er off the scent as it were
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 36797
Location: Hampshire,
United Kingdom
Thanked: 1381 times

PostPosted: Sun Dec 03, 2006 11:56 pm Reply with quote

An immersion heater is very likely to have a local DP switch for isolation. So are other fixed appliances like cookers. Non-fixed appliances will have a plug you can pull out.
Back to top
 Alert Moderators
Big_Spark

from United Kingdom

Joined: 20 Feb 2004
Posts: 3434
Location: United Kingdom
Thanked: 1 time

PostPosted: Mon Dec 04, 2006 12:11 am Reply with quote

Invisible, John is right, and as far as I am aware, to comply with Britich Standards, FCU's need to be Double Pole switched anyway, so it is likely that you would isolate the fault by turning off the offending equipment..

Could be wrong on the DP requirement for the FCU's though..anyone know the exact position on this?
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 25246
Location: Cheshire,
United Kingdom
Thanked: 445 times

PostPosted: Mon Dec 04, 2006 1:55 am Reply with quote

As far as I remember, there is no requirement to switch the neutral, but a DP switch is considered good practice.
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Shock from fully earthed sink! 8 380 Wed Aug 24, 2011 10:21 am
Lights not fully off when off ?? 7 800 Wed Nov 24, 2004 10:45 am
MK Fully populated with RCBO's (x15) 41 1500 Fri Apr 19, 2013 9:49 am
Fully loaded consumer units - ??? 6 320 Thu Feb 24, 2011 7:54 pm
Am I fully protected? 5 320 Sat Feb 05, 2011 11:15 am


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.