Joined: 26 Oct 2006 Posts: 1 Location: Warwickshire, United Kingdom Thanked: 0 times
Posted: Thu Oct 26, 2006 11:18 am Post Subject:
ELECTRIC FULLY TRIPPING OUT - please help!
Hope you can help. Our Hager consumer unit is tripping out intermittently (maybe about once a day). It is the MAIN switch that goes, not just one of the individual fuses, so we are really stumped as to where the problem could be. I have noticed over the last week that it tends to happen at about 6.30 in the morning!!! Is it possible that there is some kind of incoming surge in power at that time that results in the whole thing blowing?
Joined: 15 Apr 2005 Posts: 12857 Location: Yorkshire, United Kingdom Thanked: 22 times
Posted: Thu Oct 26, 2006 6:32 pm Post Subject:
Definitely an RCD. What sort of earth system do you have? Unless its TT, with an earth rod, theres no need for the mainswitch to be an RCD (and it shouldn't be, for the reason you've highlighted in your post - all the electric goes off it theres a fault). An electrician could alter this setup for you. I reckon your heating is set to come on at 6:30
Joined: 20 Feb 2004 Posts: 3434 Location: United Kingdom Thanked: 0 times
Posted: Sun Dec 03, 2006 8:40 pm Post Subject:
Re: ELECTRIC FULLY TRIPPING OUT - please help!
cashka76 wrote:
Hope you can help. Our Hager consumer unit is tripping out intermittently (maybe about once a day). It is the MAIN switch that goes, not just one of the individual fuses, so we are really stumped as to where the problem could be. I have noticed over the last week that it tends to happen at about 6.30 in the morning!!! Is it possible that there is some kind of incoming surge in power at that time that results in the whole thing blowing?
Hope you can help shed some light!
Claire
Claire, check the timer settings for your heating system or water heating system (Immersion), whichever you have. It could be that one of the parts of this system has developed a fault and is causing the trip.
Also, what time do you and your partner rise in the morning? Is there something about your routine that could shed some light on the matter? Do you have an electric or power shower that is invariably used at about 06:30?
Have a good think, it is likely to be something simple to identify when you check everything.
__________________ I only do commercial and Industrial so Prescott can shove his Part P tax
Joined: 25 Mar 2006 Posts: 295 Location: Essex, United Kingdom Thanked: 0 times
Posted: Sun Dec 03, 2006 9:25 pm Post Subject:
Am I right in thinking that if you were to detect the circuit of the fault (so happens to be a neutral/earth fault), then isolate via keeping mcb switched off on that circuit the fault would still trip a RCD !!!
Joined: 14 Sep 2006 Posts: 3488 Location: Gloucestershire, United Kingdom Thanked: 19 times
Posted: Sun Dec 03, 2006 9:36 pm Post Subject:
Neutral/earth fault can trip RCD with its Phase conductor isolated - it depends if there are any other circuits drawing current giving rise to imbalance in the RCD because of their neutral current leaking to earth via the fault
Joined: 25 Mar 2006 Posts: 295 Location: Essex, United Kingdom Thanked: 0 times
Posted: Sun Dec 03, 2006 9:47 pm Post Subject:
securespark wrote:
If it's an N/E fault, yes. If an L/E fault, it is possible to isolate it by switching mcb off.
The point I was getting to, is that to completely isolate a found fault (neutral/earth) not knowing the reason for it and not a plugged in item, you would have to say in a immersion heater physically un-wire the heater to stop the RCD from tripping rather than switching the MCB off, maybe a difficult task for a DIY'er, and could make tracking down a fault a bit more difficult than just isolating a circuit by switching MCB's off one by one, thus throwing a DIY'er off the scent as it were
Joined: 15 Nov 2005 Posts: 24037 Location: Hampshire, United Kingdom Thanked: 54 times
Posted: Sun Dec 03, 2006 11:56 pm Post Subject:
An immersion heater is very likely to have a local DP switch for isolation. So are other fixed appliances like cookers. Non-fixed appliances will have a plug you can pull out.
Joined: 20 Feb 2004 Posts: 3434 Location: United Kingdom Thanked: 0 times
Posted: Mon Dec 04, 2006 12:11 am Post Subject:
Invisible, John is right, and as far as I am aware, to comply with Britich Standards, FCU's need to be Double Pole switched anyway, so it is likely that you would isolate the fault by turning off the offending equipment..
Could be wrong on the DP requirement for the FCU's though..anyone know the exact position on this?
__________________ I only do commercial and Industrial so Prescott can shove his Part P tax