max load
Reply with quote Thanks

My local DIY store sells 2.5mm2 cable which it says is suitable for up to 23 amps. Why is it then that it is normal to have a 30 amp fuse on a ring main?
Also, does anyone know how to put the "2" in "mm2" in superscript?
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
ricicle

from United Kingdom

Joined: 14 Sep 2006
Posts: 3488
Location: Gloucestershire,
United Kingdom
Thanked: 19 times

PostPosted: Mon Nov 06, 2006 8:53 pm    Post Subject:
Reply with quote Thanks

The clue is in 'ring'.The theory behind it is the Ring Final Circuit is wired out from the CU, round the socket outlets and then returns to the CU.Then each leg should have an equal share of the 30/32A load ie 15/16A.That is why the ring tests are important as they ensure it is a ring and no one leg will carry a possible full 30/32A
Back to top
 Alert Moderators
Taylortwocities

from United Kingdom

Joined: 27 Jul 2006
Posts: 4939
Location: Oxfordshire,
United Kingdom
Thanked: 63 times

PostPosted: Mon Nov 06, 2006 8:59 pm    Post Subject:
Reply with quote Thanks

Hold the Alt key down and type 0178 on yr numeric keypad. When you release the Alt key you will get a ²

There lots of these. If you've got MS Word go to Insert / Symbol. As you select various symbols from the table the shortcut is displayed at the btm of the window.

º ½ ¼ ³ etc etc icon_smile.gif

TTC
Back to top
 Alert Moderators
blackfacespikeyhair

from United Kingdom

Joined: 06 Nov 2006
Posts: 12
Location: Leeds,
United Kingdom
Thanked: 0 times

PostPosted: Mon Nov 06, 2006 9:00 pm    Post Subject:
Reply with quote Thanks

Why are we limited to 30 amps then? Sounds like 46 would be ok. Also, is the load always split exactly equally in each direction around the ring, or does it depend on, say, how far around the ring the load is?
Back to top
 Alert Moderators
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4540
Location: United Kingdom
Thanked: 10 times

PostPosted: Mon Nov 06, 2006 9:12 pm    Post Subject:
Reply with quote Thanks

blackfacespikeyhair wrote:
Why are we limited to 30 amps then? Sounds like 46 would be ok. Also, is the load always split exactly equally in each direction around the ring, or does it depend on, say, how far around the ring the load is?


Balence won't be spot on (if all the heavy loads are on one side of centre it'll be quite a way off) which is why we don't double, the old rules used to say cable rateing of 2/3 fuse rateing, but now they say 20A cable rateing for upto 32A fuse IIRC (I seem to remember a 'wireing matters' article about the ammendmant)

And by the way, it has a rateing of *upto* 27A not 23A (obviously depending on how it is installed)
Back to top
 Alert Moderators
blackfacespikeyhair

from United Kingdom

Joined: 06 Nov 2006
Posts: 12
Location: Leeds,
United Kingdom
Thanked: 0 times

PostPosted: Mon Nov 06, 2006 9:22 pm    Post Subject:
Reply with quote Thanks

Thanks for all your answers by the way.

In response to Adam's comment, would it therefore be possible to overload the cable if there were, say, a 30 amp load very close to one end of the ring?

Incidentally, I got the figure of 23 from the cable packaging. I guess 27 is a peak rating whereas 23 is considered "normal use" perhaps??.
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10887
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Tue Nov 07, 2006 12:04 am    Post Subject:
Reply with quote Thanks

A ring doesn't have an end as such, the ring leaves the CU on one leg and loops to each socket in turn before returning to the CU. We limit to 32A as all of the load may not be spread earound qually around the ring circuit, infact all 32A may be loaded on the first few sockets on one side of the ring. This then relies on ohms law to spread the current through the parallel paths of the cables. This is also one reason why some here don't really like the idea of ring circuits. A spur from a ring is allowed as long as it is only feeding one point such as a socket or fused spur unit whereas the overload protection is provided by the fuses in the plugtop/fsu and short circuit protection is provided by the 32A breaker. Here is a picture of a ring final socket circuit. Hope this makes sense.
Back to top
 Alert Moderators
Adam_151

from United Kingdom

Joined: 17 Jun 2004
Posts: 4540
Location: United Kingdom
Thanked: 10 times

PostPosted: Tue Nov 07, 2006 10:12 am    Post Subject:
Reply with quote Thanks

The current in each leg is divided up in proportion to the leg length of a ring, if you put a 10A load in the middle, you'll get 5A down each side, move it to a quater way around and you get 7.5A and 2.5A, if its only a 10th of the way around you get 9A and 1A. You can't have a 30A load on a BS1363 plug obviously, but if you had 3 sockets clustered towards the end of the ring and had a 10A load on each then you could see the current divided up as something like 27A and 3A (if you had them a 10th of the way around), its almost as bad as a broken ring (where the ring accidentally becomes split somewhere along its length and is not a ring anymore)

When installing a ring, you should be careful to spead the sockets and loads out pretty evenly, no good wireing each one in turn, ending up 30m away from the fuse and putting a cable with no sockets on in to order to complete, much better to to get every second socket on the way out, and the remaining half on the way back
Back to top
 Alert Moderators
dingbat

from United Kingdom

Joined: 29 Sep 2003
Posts: 2205
Location: West Midlands,
United Kingdom
Thanked: 0 times

PostPosted: Wed Nov 08, 2006 7:07 am    Post Subject:
Reply with quote Thanks

Much better, all round, to install radial circuits, properly protected. icon_wink.gif
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Split load with two RCDs 19 820 Sun Jan 13, 2008 8:54 pm
Maximum load for three gang light switch 2 360 Fri Jan 25, 2008 12:27 pm
Load too heavy for light switch? 18 880 Tue Jan 08, 2008 3:21 pm
Electrician-fitted part-load consumer unit. 11 700 Wed Jan 02, 2008 3:01 pm
Tripping under load? 11 440 Tue Dec 11, 2007 3:07 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.