Exam help (lost my notes)

This topic originated from the How to page called Changing a fuse on the consumer unit
Click here to return to the page called Changing a fuse on the consumer unit.
Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
loola

from United Kingdom

Joined: 07 Jan 2007
Posts: 6
Location: Merseyside,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jan 07, 2007 3:27 pm    Post Subject:
Exam help (lost my notes)
Reply with quote Thanks

Hi

I need some help!! Can anybody explain the operations of the following components of an electrical distribution system please?

Main Consumer Unit
Residual Current Device
Catridge Fuse
Earth Wire

Thanks!!
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
BigJon

from United Kingdom

Joined: 18 Jun 2006
Posts: 250
Location: Glasgow,
United Kingdom
Thanked: 1 time

PostPosted: Sun Jan 07, 2007 3:37 pm    Post Subject:
Reply with quote Thanks

The regs book at the beginning lists the purposes for everything.
Or you could ask your lecturer icon_razz.gif
Back to top
 Alert Moderators
loola

from United Kingdom

Joined: 07 Jan 2007
Posts: 6
Location: Merseyside,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jan 07, 2007 3:48 pm    Post Subject:
Reply with quote Thanks

BigJon wrote:
The regs book at the beginning lists the purposes for everything.
Or you could ask your lecturer icon_razz.gif



That would be good thinking but the night before my exam and i have lost my notes it just isnt a possability!!
Back to top
 Alert Moderators
davy_owen_88

from United Kingdom

Joined: 17 Nov 2006
Posts: 1680
Location: West Glamorgan,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jan 07, 2007 3:51 pm    Post Subject:
Re: HELP
Reply with quote Thanks

loola wrote:
Hi

I need some help!! Can anybody explain the operations of the following components of an electrical distribution system please?

Main Consumer Unit
Residual Current Device
Catridge Fuse
Earth Wire

Thanks!!


Main consumer unit

The first point in the 'electric chain' of any household electricity supply (thats owned and maintained by the householder). From here all other circuits are fed and protected by the fuses/MCB's/RCD's.

RCD

A device that measures the current flowing through the phase and neutral conductors and when an imbalance is detected that exceeds the rated trip value the supply is turned off.

Catridge Fuse

A cartridge which DOESN'T accept rewirable fuse wire icon_razz.gif. Connected to the consumer unit it's purpose is to break the supply in the event of an overload. The current which blows the fuse depends on the value of fuse installed.

Earth Wire

Takes many forms including:

the main equipotential bonding conductors that connect the gas and water supply pipes to the main earthing terminal
supplementary bonding conductors that link conductive metal parts in bathrooms
the main earthing conductor connecting the main earthing terminal to the earthing point.
the earth cable as part of sheathed cables.

In all cases its used as a path for fault current (except supp. where its used to limit P.d between conductive parts to reduce the risk of shock) Earthing is needed to allow a large enough current to flow from phase to earth so that the protective devices can activate so as to remove the danger.

You might want to read the regs for the actual 'text-book' answers as what I've written will not contain all the info you need to answer your questions.

Davy

EDIT:

loola wrote:
That would be good thinking but the night before my exam and i have lost my notes it just isnt a possability!!


Well my above answers are written for joe-public to provide a basic understanding, its probably not suitable for an exam answer. I'm sure someone will come along and add bits of info or even be kind enough to write out the explanations given in the regs.


Last edited by davy_owen_88 on Sun Jan 07, 2007 4:20 pm, edited 4 times in total
Back to top
 Alert Moderators
loola

from United Kingdom

Joined: 07 Jan 2007
Posts: 6
Location: Merseyside,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jan 07, 2007 3:56 pm    Post Subject:
Re: HELP
Reply with quote Thanks

davy_owen_88 wrote:
loola wrote:
Hi

I need some help!! Can anybody explain the operations of the following components of an electrical distribution system please?

Main Consumer Unit
Residual Current Device
Catridge Fuse
Earth Wire

Thanks!!


Main consumer unit

The first point in the 'electric chain' of any household electricity supply. From here all other circuits are fed and protected by the fuses/MCB's/RCD's.

RCD

A device that measures the current flowing through the phase and neutral conductors and when an imbalance is detected that exceeds the rated trip value the supply is turned off.

Catridge Fuse

A cartridge which accepts rewirable fuse wire. Connected to the consumer unit it's purpose is to break the supply in the event of an overload. This overload depends on the value of fuse wire installed in the cartridge fuse.

Earth Wire

Takes many forms including:

the main equipotential bonding conductors that connect the gas and water supply pipes to the main earthing terminal
supplementary bonding conductors that link conductive metal parts in bathrooms
the main earthing conductor connecting the main earthing terminal to the earthing point.
the earth cable as part of sheathed cables.

In all cases its used as a path for fault current (except supp. where its used to limit P.d between conductive parts to reduce the risk of shock) Earthing is needed to allow a large enough current to flow from phase to earth so that the protective devices can activate so as to remove the danger.

You might want to read the regs for the actual 'text-book' answers as what I've written will not contain all the info you need to answer your questions.

Davy



Brilliant Thanks very much!!

Since it sounds like you know what you are talking about any idea about this one....

explain 3 functions of an electrical conduit system?

Thanks
Back to top
 Alert Moderators
CookyMan9999

from United Kingdom

Joined: 07 Jan 2007
Posts: 46
Location: Bristol,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jan 07, 2007 4:09 pm    Post Subject:
Reply with quote Thanks

LOL davvy why don't you just go and sit the exam har har


Last edited by CookyMan9999 on Sun Jan 07, 2007 4:26 pm, edited 1 time in total
Back to top
 Alert Moderators
ricicle

from United Kingdom

Joined: 14 Sep 2006
Posts: 3485
Location: Gloucestershire,
United Kingdom
Thanked: 19 times

PostPosted: Sun Jan 07, 2007 4:14 pm    Post Subject:
Re: HELP
Reply with quote Thanks

[quote="davy_owen_88]Catridge Fuse

A cartridge which accepts rewirable fuse wire. Connected to the consumer unit it's purpose is to break the supply in the event of an overload. This overload depends on the value of fuse wire installed in the cartridge fuse.

.[/quote]

Wrong - A semi-enclosed fuse accepts fuse wire, a cartridge fuse is one that cannot be re-wired and is usually of a high breaking capacity
Back to top
 Alert Moderators
davy_owen_88

from United Kingdom

Joined: 17 Nov 2006
Posts: 1680
Location: West Glamorgan,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jan 07, 2007 4:18 pm    Post Subject:
Reply with quote Thanks

CookyMan9999 wrote:
LOL davey why don't you just go and sit the exam har har


Why does everyone write 'Davey' I even write my name at the bottom of every post and its next to every post I make icon_razz.gif

And the reason I don't sit the exam is because as ricicle has pointed out, I have a tendency to confuse certain terms and make myself look like a retard, lol.


Last edited by davy_owen_88 on Sun Jan 07, 2007 4:24 pm, edited 2 times in total
Back to top
 Alert Moderators
loola

from United Kingdom

Joined: 07 Jan 2007
Posts: 6
Location: Merseyside,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jan 07, 2007 4:21 pm    Post Subject:
Reply with quote Thanks

so does anybody fancy helping me out and even letting me know what a conduit system is?

Please?!!
Back to top
 Alert Moderators
ricicle

from United Kingdom

Joined: 14 Sep 2006
Posts: 3485
Location: Gloucestershire,
United Kingdom
Thanked: 19 times

PostPosted: Sun Jan 07, 2007 4:22 pm    Post Subject:
Reply with quote Thanks

A conduit system is made up of various sizes of tube (steel/pvc) that have manufactured fittings available for direction changes, terminations etc.The tubes can be cut to length and bent as well to follow building contours.
Single, insulated cables are normally drawn into the tubes making wiring fairly easy once the tubes have been installed.
The conduit offers better mechanical protection, especially steel, than clipped cables and can be rewired fairly straightforwardly when or if needed
Special tools are required to install conduit, particularly steel, but when finished can look very neat


Last edited by ricicle on Sun Jan 07, 2007 4:28 pm, edited 1 time in total
Back to top
 Alert Moderators
loola

from United Kingdom

Joined: 07 Jan 2007
Posts: 6
Location: Merseyside,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jan 07, 2007 4:24 pm    Post Subject:
Reply with quote Thanks

ricicle wrote:
icon_wink.gif


Is that a yes?

Thanks for your help on the cartridge fuse!!
Back to top
 Alert Moderators
BigJon

from United Kingdom

Joined: 18 Jun 2006
Posts: 250
Location: Glasgow,
United Kingdom
Thanked: 1 time

PostPosted: Sun Jan 07, 2007 4:28 pm    Post Subject:
Reply with quote Thanks

A conduit system is used to run/protect single core cables
Its basically metal tubing and mainly comes in black enamel or galvanised.

*beaten by better explanation above* icon_smile.gif
Back to top
 Alert Moderators
ricicle

from United Kingdom

Joined: 14 Sep 2006
Posts: 3485
Location: Gloucestershire,
United Kingdom
Thanked: 19 times

PostPosted: Sun Jan 07, 2007 4:31 pm    Post Subject:
Reply with quote Thanks

see my edited post above, the icon_wink.gif was for davy
Back to top
 Alert Moderators
loola

from United Kingdom

Joined: 07 Jan 2007
Posts: 6
Location: Merseyside,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jan 07, 2007 4:38 pm    Post Subject:
Reply with quote Thanks

so am i right in saying that three functions of an electrical conduit system would be


1, the cables can bend to follow the contours of a building

2, the conduit offers better mechanical protection than clipped cables

3, it can be rewired fairly easily if needed.


Thanks everyone for all your help!!

I know it looks bad the night before the exam and i seem to have very little knowledge on the topic but it is just one out of 5 topics from my services exam for a construction management degree, so everyone thanks so much!!!

icon_biggrin.gif
Back to top
 Alert Moderators
ricicle

from United Kingdom

Joined: 14 Sep 2006
Posts: 3485
Location: Gloucestershire,
United Kingdom
Thanked: 19 times

PostPosted: Sun Jan 07, 2007 4:44 pm    Post Subject:
Reply with quote Thanks

Not sure about No.1 icon_confused.gif
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
guidance notes 2 280 Sat Feb 09, 2008 5:00 pm
c and g 2382 exam only 3 280 Tue Nov 04, 2008 10:20 am
on line mock exam for 17th edition regs 5 3580 Fri Oct 17, 2008 6:14 pm
2391 exam papers 2 1020 Tue May 05, 2009 5:45 pm
Multiple Choice Exam at work - can you answer this...? 16 580 Wed May 20, 2009 8:30 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.