The boiler will fire and run for a short time but then cut out. The fan and pump continue to run then after a minute or so the gas will reignite. This makes running a bath of water impossible as the water runs intermittently hot and cold.
The fault is repeatable with just CH (Winter mode, Control full) The heating will reach temperature but it takes longer as for half the time the flue exhaust is cooling the exchanger instead of gas heating.
I have followed the manufactures fault diagram but due to the intermittent nature of the problem it does not help. Thermistors and limit stat have been checked for function and are good. Diverter and micro switches function Pressure is correct for maximum and minimum gas. Pressure can be reduced at potentiometer. My thoughts are control PCB, I would appreciate another opinion before I commission the work.
Thanks
The fault is repeatable with just CH (Winter mode, Control full) The heating will reach temperature but it takes longer as for half the time the flue exhaust is cooling the exchanger instead of gas heating.
I have followed the manufactures fault diagram but due to the intermittent nature of the problem it does not help. Thermistors and limit stat have been checked for function and are good. Diverter and micro switches function Pressure is correct for maximum and minimum gas. Pressure can be reduced at potentiometer. My thoughts are control PCB, I would appreciate another opinion before I commission the work.