Shower fuse keeps blowing
Hi,
I have a 8.5kw shower, 6mm cable and a 30A cartridge fuse. The fuse blows after approx tem minutes of shower use and gives off a very fishy smell at the fuse box. I have checked all the connections and they are OK.
I have been told I really need a 45A fuse to allow full power to heat the water. Is this correct or not. I have bought a 45A fuse but it is far too big for the fuse holder meaning it must always have been a 30A fuse. Any advice appreciated.
Joined: 03 Nov 2006 Posts: 3609 Location: Bedfordshire, United Kingdom Thanked: 22 times
Posted: Fri Jan 26, 2007 2:54 pm Post Subject:
Re: Shower fuse keeps blowing
mooney3 wrote:
Hi,
I have a 8.5kw shower, 6mm cable and a 30A cartridge fuse. The fuse blows after approx tem minutes of shower use and gives off a very fishy smell at the fuse box. I have checked all the connections and they are OK.
I have been told I really need a 45A fuse to allow full power to heat the water. Is this correct or not. I have bought a 45A fuse but it is far too big for the fuse holder meaning it must always have been a 30A fuse. Any advice appreciated.
Paul
DO NOT USE THE SHOWER. Pull the fuse out to prevent it being used.
Get a QUALIFIED electrician.
The fishy smell is the result of the the fuse holder overheating and the material becoming brittle. ( the smell is a chemical evaporating from the plastic ). The fuse is glowing hot while you are showering. It is destroying the fuse holder and very likely damaging other equipment in the fuse box.
Yes the 8.5 kilowatt does need a 45 amp fuse. It also needs 45 amp cable from the fuse box to the shower.
Joined: 11 Jan 2004 Posts: 16480 Location: Cheshire, United Kingdom Thanked: 14 times
Posted: Fri Jan 26, 2007 4:18 pm Post Subject:
Should be 40A really.
However, as has been said, you can't just stick a higher device in and hope for the best. Will the consumer unit handle it? Will the cable? Will the DP switch? Will the tails, meter and main fuse?
Have you got up-to-date MEB's and supplementary in the bathroom?