Posted: Wed Feb 07, 2007 2:11 pm Post Subject:
6mm^2 twin and earth will be sufficient for a 37A load providing it isn't subject to other derating factors (high ambient temperatures, running through insulation in walls/lofts, grouping factors etc.)
Let us know how you intend to install the cable and then we can verify if 6mm^2 will be ok. It might be worth using 10mm^2 cable regardless though so if you decide to upgrade the shower in the future you don't need to rip out the old.
Joined: 14 Sep 2006 Posts: 3485 Location: Gloucestershire, United Kingdom Thanked: 19 times
Posted: Wed Feb 07, 2007 2:15 pm Post Subject:
6mm˛ will be fine on a 40Amp mcb as long as the cable doesn't follow a route through thermal insulation and is not grouped with other cables
Are you aware that this work is notifiable to your local building control under Part P of the building regs?
Most manufacturers recommend the use of a 30mA RCD to protect the circuit also and I second this as will the majority of sparks on here.
Is your local supplementary bonding up to scratch?
__________________ Empty barrels make the most noise.
Joined: 07 Feb 2007 Posts: 6 Location: Cornwall, United Kingdom Thanked: 0 times
Posted: Wed Feb 07, 2007 3:39 pm Post Subject:
Thanks for your help,what is a supplementary bonding?and why do i have to notify building control.
I shall only be laying the cables during the building stage of an en-suite,i sghall get a competant electrician to do the clever bits at the end with rcd,etc.
Joined: 17 Nov 2006 Posts: 1680 Location: West Glamorgan, United Kingdom Thanked: 0 times
Posted: Wed Feb 07, 2007 5:27 pm Post Subject:
breca wrote:
I shall only be laying the cables during the building stage of an en-suite,i sghall get a competant electrician to do the clever bits at the end with rcd,etc.
In that case don't worry about supplementary bonding and don't worry about building control - your electrician will sort all that for you.
You are very close to the limit of 6mm^2 cable. If I were you I'd put in 10mm^2 just for future proofing.