Ideal Classic Boiler

Joined
3 Mar 2007
Messages
1
Reaction score
0
Location
Cambridgeshire
Country
United Kingdom
Filling the boiler up with water to 1 bar then when boiler fires up water is coming out of pressure release valve, emptying it of the water, help any solutions already replaced pressure release valve and vessel. Boiler is 8years old but has always had this problem can you help?
 
Sponsored Links
is expansion vessel bgi enough to cope with size of heating system?
 
As above, especially as it's been doing it since it's been installed. Try draining a rad so it's half full of air, if that cures it then you need a bigger expansion vessel.
 
Sponsored Links
Did you correctly pressurise the expansion vessels?

Tony
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top