PostPosted: Sat Mar 03, 2007 9:05 pm Reply with quote

I had a Heat Line Vizo boiler installed about 4 months ago and have experienced similar problems with noise whenever it switches on/off - which is happening every few minutes. I am sure this should not be normal behaviour from a new boiler.

This week, the pilot light has decided to go off and I am at a loss as to how it should be switched back on. There is no help available on the HEAT LINE website or anywhere else. Can someone help and advise how the pilot light can be switche don again.

Thanks
_________________________________
lynda, moderator

Please note forum rule 20

The post you hi jacked is over 3 years old
Back to top
 Alert Moderators

If you do not want to see this advert, click here to login or if you are new click here to join free.
kevplumb

from United States of America

Joined: 18 May 2004
Posts: 23671
Location: Georgia,
United States of America
Thanked: 918 times

PostPosted: Sat Mar 03, 2007 9:32 pm Reply with quote

andyman6 wrote:
better that the pilot light is aimed towards burner to catch gas as i t is released from jets


tell me that is a JOKE icon_eek.gif icon_eek.gif icon_rolleyes.gif
Back to top
 Alert Moderators
ChrisR

from United Kingdom

Joined: 24 Jul 2003
Posts: 23273
Location: London,
United Kingdom
Thanked: 1034 times

PostPosted: Sun Mar 04, 2007 12:20 am Reply with quote

Quote:
Can someone help and advise how the pilot light can be switche don again.


It doesn't have a permanent pilot.
Where does the Fault Finding guide in the manual get you?
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 51199
Location: London,
United Kingdom
Thanked: 3127 times

PostPosted: Sun Mar 04, 2007 12:20 am Reply with quote

No modern boiler has had a pilot light for about 10 years!

The original posting may well be related to the Vizo which is a hybrid condensing. The Vizo is a B&Q brand version of the C24 and C28.

These boilers start an ignition spark and about 0.5 sec afterwards the gas is turned on at the preset ignition pressure. This will always ignite the gas with something of a thud but can be reduced by careful adjustment of the ignition pressure.

As these are very cheap boilers they are usually installed cheaply and its possible the gas supply pipe is undersized and contributing to the problem. As a very minimum the gas supply should be in 22 mm for the whole length.

It sounds as if the installer was not CORGI registered as the service engineer apparently came to commission it. If the installer was CORGI and it is undersized ( more than 1 mB pressure loss ) then a complaint will get the installer to correctly size it at his cost.

All modern boilers make a sound but this normal.

Tony
Back to top
 Alert Moderators
gas4you

from United Kingdom

Joined: 23 Feb 2007
Posts: 17234
Location: Norfolk,
United Kingdom
Thanked: 600 times

PostPosted: Sun Mar 04, 2007 10:29 am Reply with quote

Along Tony's, lines but has somebody ever checked the working pressure at the meter. If too low then boiler will not ignite 'first' time and gas will build up until 'thump' ignition. This should have been checked at time of installation and by heatline enginneer!
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 51199
Location: London,
United Kingdom
Thanked: 3127 times

PostPosted: Sun Mar 04, 2007 12:37 pm Reply with quote

Most manufacturer's service engineers would have checked pressure at inlet to boiler and many would check at meter as well but many dodge the issue of undersized gas supply pipes and dont even point it out to the customer.

I dont know why because I think they have a duty of care to the owner and they need to cover their own backs in case CORGI come to inspect. So I would always mention it to the owner and write it on the report. CORGI class an undersized gas supply as At Risk !

With conventional burners its not very sensitive to supply pressure variations but if the owner is concerned by the ignition thump then all aspects should have been checked.

A simple test the owner could make is to turn cooker burners on full and see if that makes any difference to the boiler start up noise. That would eliminate a sluggish meter regulator.

One assumes the Heatline service agent at least checked the ignition pressure and placement of the electrodes.

Tony
Back to top
 Alert Moderators
Search this topic :: View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
heat line vizo problem 15 2100 Mon Dec 08, 2008 9:31 am
Heat Line Vizo 24 keeps blowing fuse 6 60 Mon Feb 18, 2013 3:36 pm
heat line vizo HELP 9 760 Mon Dec 29, 2008 5:35 pm
heat line vizo 24 13 1220 Tue Nov 23, 2010 10:28 pm
Heat line vizo 24 18 6160 Fri Oct 12, 2007 3:20 pm


 
DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
Network | Advertising | Newsletter
DIY | DIY How To | @home | DIY Wiki | DIY Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy. Copyright © 2000-2014 DIYnot Limited.