PostPosted: Mon Mar 05, 2007 12:20 pm    Post Subject:
Immersion Heater
Reply with quote Thanks

Hello, Would be grateful of some advice, I am looking to install a second immersion heater element as a backup should the Central Heating system breakdown. In terms of connecting it to the household electrical supply, can I spur off a plug socket to provide the supply ????. If not what would you suggest.

Thanks ;-}}}}}}
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
Chri5

from United Kingdom

Joined: 19 Jan 2007
Posts: 1827
Location: London,
United Kingdom
Thanked: 28 times

PostPosted: Mon Mar 05, 2007 12:37 pm    Post Subject:
Reply with quote Thanks

Whats the size of each element in watts, and is the element already in use on it's own circuit and fused at the CU seperately?

Do you have any idea what the cable size is on the existing element?
Back to top
 Alert Moderators
ICARUS

from United Kingdom

Joined: 05 Mar 2007
Posts: 6
Location: Cheshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Mar 05, 2007 1:29 pm    Post Subject:
ANSWER
Reply with quote Thanks

Chri5 wrote:
Whats the size of each element in watts, and is the element already in use on it's own circuit and fused at the CU seperately?

Do you have any idea what the cable size is on the existing element?


Hello, It is a new element that I want to add to the water cylinder, its rating is 3KW, I am unsure as to whether the existing element is fused seperately. There is no indication of this on the CU.

Cheers
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12852
Location: Yorkshire,
United Kingdom
Thanked: 22 times

PostPosted: Mon Mar 05, 2007 3:20 pm    Post Subject:
Reply with quote Thanks

One immersion heater should provide more than enough hot water, in the event of a boiler breakdown. Why have 2 'mersions? And whats the chances of a boiler breakdown? If it does breakdown, it'll probably be working again within 24 hours. icon_razz.gif

And the first 'mersion should be on its own circuit, as will this new one you are wanting to install.
Back to top
 Alert Moderators
Spark123

from United Kingdom

Joined: 02 Jun 2005
Posts: 10887
Location: Cumbria,
United Kingdom
Thanked: 39 times

PostPosted: Mon Mar 05, 2007 3:30 pm    Post Subject:
Reply with quote Thanks

It is not normal practice to supply an immersion heater from a socket circuit, they are normally connected to their own radial circuit.
Back to top
 Alert Moderators
ICARUS

from United Kingdom

Joined: 05 Mar 2007
Posts: 6
Location: Cheshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Mar 05, 2007 4:03 pm    Post Subject:
Immersion Heater
Reply with quote Thanks

Hello,

The reason why I am wanting to install a second immersion heater is that the current one is controlled by the boiler / timer and cannot work independently. i.e if the boiler does not fire up you cannot turn on the water immersion heater.

The boiler has broken quite a few times and it means that we are left without hot water even with British Gas cover for at least two Days if not more if they don't have the parts.

So I want an independent immersion heater that I can just switch on if the boiler packs up.

Cheers
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Mon Mar 05, 2007 4:08 pm    Post Subject:
Reply with quote Thanks

If you are sure it is an ordinary electric immersion heater that is already installed in your hot water cylinder, then a better solution would be to have it rewired in the usual way - that is, with a separate radial circuit fused at 15 or 16Amps from your consumer unit. It does not have to go through your boiler controller. This can have a timeswitch or a plain switch which is normally placed in the airing cupboard adjacent to the cylinder.

If you are not experienced at electrical work it would be better to have a recommended local electrician do it. installing a new circuit is notifiable work. I would have expected a dedicated circuit to have been installed already if it is a reasonably modern house, but I gather you can't see one.

It is not correct to supply an immersion heater from the socket ring circuit.
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Mon Mar 05, 2007 4:11 pm    Post Subject:
Reply with quote Thanks

i think a second immersion heater is overkill

personally i'd put a plug on the existing immersion heater and then have a pair of sockets, one connected to the existing supply for the immersion heater and one wired on the upstairs ring in the normal way.

then when the heating system dies just unplug the immersion heater and plug it in directly.

its not best practice to have an immersion on the ring but since the setup is only for occasional use and upstairs rings are rarely heavilly loaded it shouldn't be a major problem.
Back to top
 Alert Moderators
ICARUS

from United Kingdom

Joined: 05 Mar 2007
Posts: 6
Location: Cheshire,
United Kingdom
Thanked: 0 times

PostPosted: Mon Mar 05, 2007 4:19 pm    Post Subject:
Reply
Reply with quote Thanks

plugwash wrote:
i think a second immersion heater is overkill

personally i'd put a plug on the existing immersion heater and then have a pair of sockets, one connected to the existing supply for the immersion heater and one wired on the upstairs ring in the normal way.

then when the heating system dies just unplug the immersion heater and plug it in directly.

its not best practice to have an immersion on the ring but since the setup is only for occasional use and upstairs rings are rarely heavilly loaded it shouldn't be a major problem.


This sounds like a good idea, so are you saying that I should attach a domestic plug to the immersion heater coax, and then install two domestic sockets one making use of current Immersion heater electrical supply and one connected to the upstairs ring and then just unplug and plug accordingly ?. icon_smile.gif
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Mon Mar 05, 2007 4:23 pm    Post Subject:
Re: Reply
Reply with quote Thanks

ICARUS wrote:

This sounds like a good idea, so are you saying that I should attach a domestic plug to the immersion heater coax, and then install two domestic sockets one making use of current Immersion heater electrical supply and one connected to the upstairs ring and then just unplug and plug accordingly ?. icon_smile.gif

its not coax its heat resistant mains flex but yes that is what i am suggesting.
Back to top
 Alert Moderators
kevnurse

from United Kingdom

Joined: 14 Oct 2006
Posts: 413
Location: Moray,
United Kingdom
Thanked: 3 times

PostPosted: Mon Mar 05, 2007 5:56 pm    Post Subject:
Reply with quote Thanks

I'm confused. I've never heard of a gas powered water boiler not using its own hot water to supply a primary heater in the DHW tank. Are you telling us that the boiler timer switches an electrical supply to your hot water tank? That is a very expensive way to routinely heat water. 1 kw/hr is 1 unit, so you're spending approx 24p per hour to heat your water (I accept that it takes less than 1 hr to bring the tank up to temperature) Furthermore, if your normal imm heater is 3 kW, you should not be passing that kind of load through a boiler timer.

I hesitate to ask this, but are you absolutely sure that you have an electric immersion heater as your normal hot water heater?
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Mon Mar 05, 2007 5:59 pm    Post Subject:
Reply with quote Thanks

Can you post a picture of the hot water cylinder, showing the pipes and cables going into it?

We like pictures!
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16485
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Mon Mar 05, 2007 8:44 pm    Post Subject:
Reply with quote Thanks

I'm confused, too!

Boiler programmers are limited to 3A maximum, so cannot control anything other than boiler, stats & pumps, etc...

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12852
Location: Yorkshire,
United Kingdom
Thanked: 22 times

PostPosted: Mon Mar 05, 2007 9:24 pm    Post Subject:
Reply with quote Thanks

securespark wrote:
I'm confused, too!

Boiler programmers are limited to 3A maximum, so cannot control anything other than boiler, stats & pumps, etc...

. . . contactors, relays etc . . .


icon_lol.gif
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Mon Mar 05, 2007 9:30 pm    Post Subject:
Reply with quote Thanks

maybe it isn't really an immersion heater.

Roll on the photos!
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
E7 immersion heater problem 2 180 Fri Feb 22, 2008 12:08 pm
Quick Immersion Heater question - rewiring help needed 13 580 Mon Jan 21, 2008 2:30 pm
immersion heater/FCU 8 182 Mon Jan 28, 2008 5:33 pm
immersion heater with boost 2 300 Sun Jan 13, 2008 8:35 pm
Immersion Heater Electrics 5 400 Fri Jan 11, 2008 12:32 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.