Old lighting circuit without earth
Reply with quote Thanks

I am adding an extractor fan to an existing lighting circuit. The existing wiring is all 2 core (Red & black) with NO earth. 1960s build. The fan is double-insulated and has no earth terminal. Is it ok to add the spur, FCU etc. without any earth connection OR is it necessary to add a new earth cable from the CU to the new spur OR is it necessary to replace all the wiring from the CU? Thanks.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
davy_owen_88

from United Kingdom

Joined: 17 Nov 2006
Posts: 1680
Location: West Glamorgan,
United Kingdom
Thanked: 0 times

PostPosted: Tue Mar 06, 2007 4:41 pm    Post Subject:
Reply with quote Thanks

If the fan doesn't require an earth and assuming you are not connecting a metal FCU/switch then there is no point in replacing the cable only to leave the earth disconnected.

Having no earth in the lighting circuit though does indicate an aged installation so it would be a good idea to get the circuits integrity checked out.

Is this fan going in the bathroom or kitchen? If so it is notifiable work.

Davy
Back to top
 Alert Moderators
plugwash

from United Kingdom

Joined: 28 Mar 2004
Posts: 6930
Location: United Kingdom
Thanked: 15 times

PostPosted: Tue Mar 06, 2007 4:44 pm    Post Subject:
Reply with quote Thanks

personally i'd say wire the fan with 2 core flex, earths that aren't actually connected to earth are a bad thing.

and make sure you use plastic boxes or screwcaps
Back to top
 Alert Moderators
bam

from United Kingdom

Joined: 06 Mar 2007
Posts: 3
Location: Bristol,
United Kingdom
Thanked: 0 times

PostPosted: Tue Mar 06, 2007 4:54 pm    Post Subject:
Reply with quote Thanks

Thanks.
I've chosen an in-line timer fan that is mounted in the loft above the bathroom ceiling to avoid the notification requirement. I'm using all plastic SW & FCU with 3A fuse to isolate both the fan and bathroom light and pull-switch (the latter is required by the fan) and 1.5mm twin & earth.

I concur that it could be misleading to someone in the future if the new cables' earth is not connected to anything. I've already done the wiring though so I'd rather not replace it all at this stage. I have run T&E from an existing rose to the SW-FCU. The earth connects to the rose earth terminal, that has no other connections.

Is having unconnected earth ok legally? What is good practice?
Back to top
 Alert Moderators
Reg_Prescott

from United Kingdom

Joined: 10 Feb 2005
Posts: 62
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue Mar 06, 2007 10:35 pm    Post Subject:
Reply with quote Thanks

plugwash wrote:
personally i'd say wire the fan with 2 core flex, earths that aren't actually connected to earth are a bad thing.

and make sure you use plastic boxes or screwcaps


Plugwash or anyone icon_biggrin.gif where can I get hold of screw caps for plastic light switches, or even plastic light switches with screw caps included? I am in a simliar position having moved into a 1960s house with no earth on the down stairs lighting cct. I have replaced all the light fittings and switches with plastic, but the back boxes are metal and I appreciate the possiblity the screws could become live in the event of a fault. Sorry to hijack the thread icon_biggrin.gif

Regards,

Mark

__________________
Here we have our old friend, the circular saw - AARRGGHH!!!
Back to top
 Alert Moderators
bam

from United Kingdom

Joined: 06 Mar 2007
Posts: 3
Location: Bristol,
United Kingdom
Thanked: 0 times

PostPosted: Wed Mar 07, 2007 8:42 pm    Post Subject:
Reply with quote Thanks

Thanks for your comments everyone. I decided that installing a new spur, or any new circuit, needs to follow modern conventions regardless of the existing wiring. I also decided that it is unacceptable to provide a "false" earth because that could be mistaken for a true earth in the future.

Fortuitously, an electric shower spur (unused) ran via the loft and is T&E and is earthed at the fuse box. I used a terminal box to terminate this spur in the loft. I then ran a single earth wire (green/yellow sleeve) the short distance from this box to the new fan spur.

I am happy that the new fan/light spur for the bathroom is now safe. The rest of the lighting circuit is earthless as before but the task of replacing all the wiring is onerous. I suppose that one should avoid using any light fixtures that are not double-insulated and, for complete safety, put those aforementioned screw caps on the light switches. Having said that I don't believe there have been any electrocutions in the house since it was built in the 1960s!
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Earth / Neutral fault on Lighting Circuit 9 1140 Sun Dec 07, 2008 3:09 pm
Earth problem in lighting circuit? 8 760 Sun Apr 02, 2006 11:06 pm
5A lighting circuit, connect L and N or L, N and earth? 9 1180 Fri Feb 16, 2007 12:01 pm
No earth on lighting circuit - new kitchen light required 5 220 Fri Nov 28, 2008 3:05 pm
Lighting Circuit earth 6 440 Fri Jul 07, 2006 3:42 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.