MY TRITON 80 9.5W ELECTRIC SHOWER IS WIRED STRIGHT FROM THE MAIN FUSE BOX 40 AMP .STRIGHT INTO TRITON SHOWER IN BATHROOM IN PLASTIC TRUNKING,NO SWITCH OR SAFTY CUTOUTS ECT ,SHOULD I CHANGE THE WAY IT HAS BEEN INSTALLED,OR LEAVE IT ALONE,I WOULD LIKE TO CHANGE IT FOR PIECE OF MIND,SO WHAT IS THE BEST AND CHEAPEST WAY ,AT PRESENT THE FUSES ARE 30AMP IN FUSEBOX,PLEASE MAKE ANY HELPFUL COMMENTS EASY TO UNDERSTAND IE STEP BY STEP FROM FUSEBOX TO SHOWER UNIT CHEERS |
|
Steve

Joined: 15 Apr 2005 Posts: 12845 Location: Yorkshire, United Kingdom Thanked: 21 times
|
Posted: Thu Mar 15, 2007 3:28 pm Post Subject: |
 |
|
stop SHOUTING
Do you know what size cable was used?
You say it goes "straight from the main fuse box 40amp"
Then you say "at present the fuses are 30amp in fusebox"
1. I hope they aren't ALL 30 amp,
2. What size fuse really feeds this shower?
3. What colour and make is the fuse box? Can you post a picture? |
|
RF Lighting

Joined: 31 Mar 2006 Posts: 10752 Location: Birmingham, United Kingdom Thanked: 73 times
|
|
casinojoe1

Joined: 11 Feb 2007 Posts: 24 Location: Manchester, United Kingdom Thanked: 0 times
|
|
securespark

Joined: 11 Jan 2004 Posts: 16480 Location: Cheshire, United Kingdom Thanked: 14 times
|
Posted: Thu Mar 15, 2007 9:19 pm Post Subject: |
 |
|
9.5kW @ 230V is 41.3A.
Chances are your circuit is wired in 6mm˛. This is only rated to 38A where trunking is installed.
Sounds like the supply is not up to the job. You also need RCD protection (to comply with manufacturer's instructions) and a local isolator (to comply with 7671). Send in some pictures. We can't advise further without them. __________________ As George Michael once said, "..if you're gonna do it, do it right, right?" |
|