my brother's shower

This topic originated from the How to page called Choosing the correct size cable
Click here to return to the page called Choosing the correct size cable.
Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
CharlesM

from United Kingdom

Joined: 15 Mar 2007
Posts: 2
Location: Plymouth,
United Kingdom
Thanked: 0 times

PostPosted: Thu Mar 15, 2007 8:03 pm    Post Subject:
my brother's shower
Reply with quote Thanks

My brother has 10.5kW shower and it keeps on tripping the fuse. It has a 30A fuse and the 6mm cable is about 20m from the consumer unit. My Dad thinks that putting in a 45A fuse may be dangerous as he doesn't think the 6mm cable would be man enough to take such a current. Do you think that he will have to upgrade the cable to a 10mm one if he puts in a 45A fuse?
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
ricicle

from United Kingdom

Joined: 14 Sep 2006
Posts: 3485
Location: Gloucestershire,
United Kingdom
Thanked: 19 times

PostPosted: Thu Mar 15, 2007 8:26 pm    Post Subject:
Reply with quote Thanks

6mm˛ is rated at 46A so as long as the cable is not installed in thermal insulation anywhere, is not likely to be in ambient temps of >30c then fitting a 45A cartridge fuse or MCB will be ok.(I take it the shower is already protected by a 30mA RCD)

__________________
Empty barrels make the most noise.


Last edited by ricicle on Thu Mar 15, 2007 8:34 pm, edited 1 time in total
Back to top
 Alert Moderators
davy_owen_88

from United Kingdom

Joined: 17 Nov 2006
Posts: 1680
Location: West Glamorgan,
United Kingdom
Thanked: 0 times

PostPosted: Thu Mar 15, 2007 8:27 pm    Post Subject:
Reply with quote Thanks

Under certain circumstances 6mm˛ is ok for 45A. The best solution though is to replace the cable with 10mm˛.

If you have a 30A fuse you most probably don't have RCD protection and an old consumer unit. Could you post some pictures?
Back to top
 Alert Moderators
CharlesM

from United Kingdom

Joined: 15 Mar 2007
Posts: 2
Location: Plymouth,
United Kingdom
Thanked: 0 times

PostPosted: Thu Mar 15, 2007 8:38 pm    Post Subject:
Reply with quote Thanks

Thanks, ricicle and Davy. I'll see if I can get a picture - of the consumer unit I assume?
Back to top
 Alert Moderators
davy_owen_88

from United Kingdom

Joined: 17 Nov 2006
Posts: 1680
Location: West Glamorgan,
United Kingdom
Thanked: 0 times

PostPosted: Thu Mar 15, 2007 8:40 pm    Post Subject:
Reply with quote Thanks

CharlesM wrote:
I'll see if I can get a picture - of the consumer unit I assume?


Yup. Should give us an idea of whether it is suitable for such a load.

You've also got over 6V of volt drop (if my memory serves me well), depending on the voltage drop in the rest of the installation you are pretty close to the limit.
Back to top
 Alert Moderators
Softus

from United Kingdom

Joined: 21 Oct 2004
Posts: 19532
Location: United Kingdom
Thanked: 6 times

PostPosted: Thu Mar 15, 2007 8:59 pm    Post Subject:
Reply with quote Thanks

davy_owen_88 wrote:
You've also got over 6V of volt drop (if my memory serves me well), depending on the voltage drop in the rest of the installation you are pretty close to the limit.

Just curious davy_owen_88 - what's the effect of exceeding that limit?
Back to top
 Alert Moderators
davy_owen_88

from United Kingdom

Joined: 17 Nov 2006
Posts: 1680
Location: West Glamorgan,
United Kingdom
Thanked: 0 times

PostPosted: Thu Mar 15, 2007 9:00 pm    Post Subject:
Reply with quote Thanks

It' isn't a problem for showers except they will warm the water a tiny bit less. But you will be exceeding the limit set by BS7671 so run for the hills icon_lol.gif
Back to top
 Alert Moderators
Softus

from United Kingdom

Joined: 21 Oct 2004
Posts: 19532
Location: United Kingdom
Thanked: 6 times

PostPosted: Thu Mar 15, 2007 9:03 pm    Post Subject:
Reply with quote Thanks

davy_owen_88 wrote:
...run for the hills icon_lol.gif

Um, excuse me being so naive, but is this because it would contravene a standard or because it would be dangerous (or both)?
Back to top
 Alert Moderators
davy_owen_88

from United Kingdom

Joined: 17 Nov 2006
Posts: 1680
Location: West Glamorgan,
United Kingdom
Thanked: 0 times

PostPosted: Thu Mar 15, 2007 9:06 pm    Post Subject:
Reply with quote Thanks

It wouldn't be dangerous in the case of a shower but if the VD exceeds the 4% limit set out in BS7671 then you have failed to meet one of its 'rules' Motors are more susceptible to VD and can fail to start because of their high in-rush currents.
Back to top
 Alert Moderators
Softus

from United Kingdom

Joined: 21 Oct 2004
Posts: 19532
Location: United Kingdom
Thanked: 6 times

PostPosted: Thu Mar 15, 2007 9:07 pm    Post Subject:
Reply with quote Thanks

Sorry to keep going on about this, but what is the purpose of that rule?
Back to top
 Alert Moderators
davy_owen_88

from United Kingdom

Joined: 17 Nov 2006
Posts: 1680
Location: West Glamorgan,
United Kingdom
Thanked: 0 times

PostPosted: Thu Mar 15, 2007 9:09 pm    Post Subject:
Reply with quote Thanks

Motors are more susceptible to VD and can fail to start due of their high in-rush currents.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16480
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Thu Mar 15, 2007 9:10 pm    Post Subject:
Reply with quote Thanks

ricicle wrote:
6mm˛ is rated at 46A so as long as the cable is not installed in thermal insulation anywhere, is not likely to be in ambient temps of >30c then fitting a 45A cartridge fuse or MCB will be ok.(I take it the shower is already protected by a 30mA RCD)


Or grouped or run in MT...

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
Softus

from United Kingdom

Joined: 21 Oct 2004
Posts: 19532
Location: United Kingdom
Thanked: 6 times

PostPosted: Thu Mar 15, 2007 9:13 pm    Post Subject:
Reply with quote Thanks

OK. Thanks. icon_smile.gif
Back to top
 Alert Moderators
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Thu Mar 15, 2007 9:15 pm    Post Subject:
Reply with quote Thanks

The problem is that for example if the shower heater element (or whatever the load is) is 10kW then at 240V it will use 41.7A, but if the cable run is too long the and the volts drop to say 220V then the current rises to 45.5A.

It only needs a VD of 8% to drop to 220V.

__________________
I downlights
Back to top
 Alert Moderators
ricicle

from United Kingdom

Joined: 14 Sep 2006
Posts: 3485
Location: Gloucestershire,
United Kingdom
Thanked: 19 times

PostPosted: Thu Mar 15, 2007 9:17 pm    Post Subject:
Reply with quote Thanks

Rotor overheating can also occur in induction motors due to undervoltage.
I can't quite remember the exact explanation but I know the rotor currents have to increase to offset the fact that the flux is lower from the stator due to reduced voltage. (I can dig out the exact explanation if anyones sad enough to be interested)

__________________
Empty barrels make the most noise.
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Another shower cable query! 2 380 Wed Jan 09, 2008 2:40 am
Old consumer units and electric shower 5 460 Tue Jan 08, 2008 1:02 pm
Wiring Shower 5 300 Mon Jan 07, 2008 2:20 pm
Connect Underfloor Heating from Shower Swicth 12 800 Wed Jan 09, 2008 3:42 pm
Shower fairies! 7 440 Wed Jan 09, 2008 9:00 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.