Joined: 23 Mar 2007 Posts: 1 Location: London, United Kingdom Thanked: 0 times
|
Posted: Fri Mar 23, 2007 10:25 am Post Subject: Cold rad and pipes, new system |
 |
|
Have a brand new CH system. All working fine apart from one rad which is cold. Pipes to and from it also cold. Is there a valve or something I need to turn to activate that rad?
Would normally call builder back to fix it, but am currently in legal dispute with them. |
|
2face

Joined: 07 Sep 2006 Posts: 322 Location: Sheffield, United Kingdom Thanked: 0 times
|
Posted: Fri Mar 23, 2007 10:56 am Post Subject: |
 |
|
shut all the rads off appart from the cold 1 .. let it run till both pipes are red hot .. equal temp..
also check the valves are both open ..
if there is a trv on the rad remove the top and check the movement of the pin .. __________________ plumbing,heating,solid fuel and electrical services. |
|