i need to install a shaver socket into my bathroom i need some info on where to pick up my power supply from eg;ring main does it need to be fused seperatley & at what rating. where i plan to mount the shaver socket there is a double socket on the other side of the wall can i tag off this. |
|
RF Lighting

Joined: 31 Mar 2006 Posts: 10752 Location: Birmingham, United Kingdom Thanked: 73 times
|
|
Spark123

Joined: 02 Jun 2005 Posts: 10887 Location: Cumbria, United Kingdom Thanked: 39 times
|
Posted: Tue Mar 27, 2007 11:41 pm Post Subject: |
 |
|
The power can come from either the lighting circuit or via a fused spur unit from the ring socket circuit. The shaver socket needs to be an isolation transformer type. The circuit it is fed from needs to be included in the supplementary bonding. These item(s) should only be installed in zone 3 or beyond. This work is notifiable to your local area building control office under part p of the building regs. |
|