extra radiator problem
Ive just fitted an extra radiator, i have taken the feed and return from existing rad pipes in the loft, the problem is that the radiator hardly gets warm, i have bled it and the system etc.
Joined: 28 Mar 2007 Posts: 3 Location: Nottinghamshire, United Kingdom Thanked: 0 times
Posted: Wed Mar 28, 2007 6:17 pm Post Subject:
Fluffster wrote:
What type of system is it ? do you have a feed and expansion tank in the loft?
Have you tried increasing your pump speed?
Pete
Its a sealed system i.e with a combi boiler, i cant understand it because the other two radiators get as hot as they always did, the other is stone cold. I think I know how to adjust the pump speed, is it the large grooved disc on the end?
Joined: 28 Mar 2007 Posts: 3 Location: Nottinghamshire, United Kingdom Thanked: 0 times
Posted: Wed Mar 28, 2007 6:21 pm Post Subject:
gas4you wrote:
Try turning off all other rads and see if this will push water to it. May be an air lock in the pipework in the loft
Yes, sorry i forgot to say, if i turn the others off then it gets hot, it appears to be bled OK, however I can hear air in the pipes (only when the other rads are off though), i have used speedifit pipe by the way...
Joined: 20 Mar 2007 Posts: 242 Location: Buckinghamshire, United Kingdom Thanked: 0 times
Posted: Wed Mar 28, 2007 8:14 pm Post Subject:
Sounds like air in the pipe still.
You will also need to balance the rads to give a little more bias to the new one
A couple of air bleeds would certainly help
Try running with only that rad on (from that circuit) for a while it may push the air out after a bit