PostPosted: Thu Apr 26, 2007 12:38 pm    Post Subject:
single oven and ceramic hob
Reply with quote Thanks

i have just purchased a neff 1422 single oven 2.7kw and a cda ceramic hob 6,800w i have a exsisting cooker 40amp radial cicuit to a cooker control unit with 45amp dp switch and 13amp socket. my questio is can i plug the neff single oven into the 13amp socket and connect the hob to the cooker switch?
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
RMS

from United Kingdom

Joined: 08 May 2006
Posts: 409
Location: United Kingdom
Thanked: 1 time

PostPosted: Thu Apr 26, 2007 12:53 pm    Post Subject:
Reply with quote Thanks

The hob could draw 6800/230 = 29.6amps

The single oven could draw 2700/230 = 11.7amps

Total possible load = 41.3 amp.

This is bad design as the protective device is only rated at 40amps and your design current exceeds this value.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16491
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Thu Apr 26, 2007 1:18 pm    Post Subject:
Reply with quote Thanks

RMS - You have not explored the possibility of diversity.

These appliances will cycle, too.

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Thu Apr 26, 2007 1:21 pm    Post Subject:
Reply with quote Thanks

The answer to your question is "yes" though I don't like sockets on cooker switches.
Back to top
 Alert Moderators
RMS

from United Kingdom

Joined: 08 May 2006
Posts: 409
Location: United Kingdom
Thanked: 1 time

PostPosted: Thu Apr 26, 2007 1:35 pm    Post Subject:
Reply with quote Thanks

Fair comment,

just don't like the idea of the single oven connected into the socket as both appliances will be used together frequently.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16491
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Thu Apr 26, 2007 7:24 pm    Post Subject:
Reply with quote Thanks

As they would be if you connected both to the cooker circuit. Look at a single oven & hob as a total load < most freestanding cookers.

If you're curious, connect a clamp-on to the cooker cable next time it's in use & see what the loading is.

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Thu Apr 26, 2007 7:38 pm    Post Subject:
Reply with quote Thanks

I don't usually approve of the diversity rules for cooking appliances, on the grounds that, come Christmas day, you will have everything on at once.

However, in this case, the max demand is so close to the MCB rating that I wouldn't be concerned. And it can only take max demand for a short time, while all elements are coming to temp.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16491
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Thu Apr 26, 2007 7:45 pm    Post Subject:
Reply with quote Thanks

I am running a 9,5 shower on a 40A Hager breaker & regularly have it on in xs of 30 mins. Never tripped yet. icon_wink.gif

__________________
As George Michael once said, "..if you're gonna do it, do it right, right?"
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
single oven and ceramic hob 6 520 Sat Aug 26, 2006 3:22 pm
Single Oven + ceramic hob 7 4900 Fri Aug 13, 2004 10:46 am
13 Amp Single Oven connection with ceramic hob 3 400 Tue May 27, 2008 10:56 pm
Installing ceramic hob and double oven 17 800 Mon Apr 28, 2008 10:20 pm
wiring a built in oven and a seperate ceramic hob 2 1560 Tue Apr 01, 2008 2:44 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.