Joined: 15 May 2007 Posts: 4 Location: Hampshire, United Kingdom Thanked: 0 times
Posted: Tue May 15, 2007 9:15 am Post Subject:
AEG 78001KF-N induction hob
This model is rated at 7.4kW. I have run a new 6mm cable 15 metres long from a 40 amp mcb to a 45 amp DP cooker switch. My problem is that the flex that came fitted to the hob has four wires...y/g, brown, blue and black. It seems clear that y/g is earth, blue is neutral and brown live but what is the black for? I've tried AEG and Service Force and they are most unhelpful.Your help would be appreciated
Joined: 15 May 2007 Posts: 4 Location: Hampshire, United Kingdom Thanked: 0 times
Posted: Tue May 15, 2007 11:02 am Post Subject:
the instructions state that it must be fitted by a qualified electrician, that the electrical mains terminal is live(!) and that a strain relief clamp should be used. This is as far as it goes.
Joined: 15 May 2007 Posts: 4 Location: Hampshire, United Kingdom Thanked: 0 times
Posted: Tue May 15, 2007 11:56 am Post Subject:
it was purchased from empire direct, a well known, UK based internet shop and delivered from AEG themselves. There is no indication of it being anything other than single phase, it is in AEG's ordinary catalogue along with other domestic appliances. There are no commercial appliances in this catalogue.
Joined: 15 Apr 2005 Posts: 12857 Location: Yorkshire, United Kingdom Thanked: 22 times
Posted: Tue May 15, 2007 8:11 pm Post Subject:
keith123 wrote:
it was purchased from empire direct, a well known, UK based internet shop and delivered from AEG themselves. There is no indication of it being anything other than single phase, it is in AEG's ordinary catalogue along with other domestic appliances. There are no commercial appliances in this catalogue.
Even so, many domestic appliances are 2- or 3-phase rated, for the european market, where residential cooker circuits are often 2- or 3- phase.
Joined: 15 May 2007 Posts: 4 Location: Hampshire, United Kingdom Thanked: 0 times
Posted: Wed May 16, 2007 9:55 am Post Subject:
Further to all the foregoing, I have now spoken to AEG ( this time someone helpful) and it appears that I have been sent the continental version. UK models are identical but do not come with a cable. I am now advised that this model will be fine, all that is neede is to connect both live wires ( brown and black to the live terminal.
Thanks for your help
Keith
Joined: 23 May 2007 Posts: 1 Location: Essex, United Kingdom Thanked: 0 times
Posted: Wed May 23, 2007 10:48 am Post Subject:
AEG Customer Service
Just to say, am having same problem with 68002KF-N hob. No sensible instructions how to connect in UK. There is no bridge between 1 and 2 and terminals are not big enough to accept cable from mains and a bridging cable. AEG customer service said they would not give any advice - now their policy.
Joined: 06 Dec 2008 Posts: 1 Location: Berkshire, United Kingdom Thanked: 0 times
Posted: Sat Dec 06, 2008 12:58 pm Post Subject:
Bridging terminals 1+2
In case anyone comes back to this post looking for an answer:
I just installed an AEG induction hob and it was supplied with a metal connector for bridging terminals 1 and 2. There definitely wasn't space in the terminal block housing to bridge using cable.