PostPosted: Tue May 29, 2007 12:37 pm    Post Subject:
central heating
Reply with quote Thanks

Cold radiators, The system is on an electonic timer for water & heating, it would appear that the radiators will only work when the system is heating the water, once the water is hot enough the radiators go cold ! pump seems to be ok as does the thermostat also no air in rads or pump, header tank also ok, not sure about the y valve, system has been ok for a couple of years and timer also seems ok, Help
Thanks
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
ChrisR

from United Kingdom

Joined: 24 Jul 2003
Posts: 18661
Location: London,
United Kingdom
Thanked: 62 times

PostPosted: Tue May 29, 2007 1:06 pm    Post Subject:
Reply with quote Thanks

Either a faulty 3 port valve or it's wrongly wired, which is very common.

see http://content.honeywell.com/uk/homes/Catalogue/Sundial%20Plans/3.4%20Y%20Plan.pdf
Back to top
 Alert Moderators
MANDATE

from United Kingdom

Joined: 06 Mar 2003
Posts: 1496
Location: Manchester,
United Kingdom
Thanked: 10 times

PostPosted: Tue May 29, 2007 9:47 pm    Post Subject:
Reply with quote Thanks

I would agree with ChrisR.
Sounds as though the valve is either moving to the CH position but not firing boiler because there is no output voltage from the valves orange wire due to faulty microswitch within valve head.
Or the valve is not moving to the CH position to trigger the microswitch, this could be a fault in wiring where there is no power on the grey wire of the valve which is needed to drive the motor from mid position to CH position.
Or motor within valve faulty and unable to overcome the resistance of the fairly strong return spring.
You should be able to remove valve head off spindle and try the various positons and verify the various movements. Only expect valve to move after few seconds delay. Also! if at CH positon and you switch off both HW and CH dont expect valve to move at all. It will not move from CH until HW is called for. Of course if all power is removed from programmer, the grey wire becomes dead and in this condition valve will return to start positon ie HW.
icon_rolleyes.gif icon_rolleyes.gif icon_rolleyes.gif
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Central heating ok but no hot water. Zone valve problem? 5 380 Fri Apr 25, 2008 7:31 am
Ripping out central heating 18 740 Fri Apr 25, 2008 4:38 pm
central heating controller 2 200 Mon Apr 21, 2008 9:01 pm
New central heating system 3 260 Mon Apr 21, 2008 1:11 pm
Noise of central heating pump vibrating through my wall! 7 1340 Sun Apr 20, 2008 3:25 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.