hi all need some help with a vaillant eco tec plus 618
It is plumbed into a sealed system with three zones, 1 x hw and 2 x CH.
On start up it has always been temperamental in that; if it starts on HW only chances are it will run ok and the HW system works as you would expect. there is an auto air vent on the flow to the cylinder
If it starts on any other zone, it will fail to start up quoting fault f75 (this means (no pressure rise was detected on turning on the pump) the cause in the manual states (water pressure sensor and or pump defective. too little water in appliance: connect external expansion vessel to return) I don't believe there is a need for an further expansion vessel as the pressure rise when hot is minimal.
I believe the pump works fine because when the appliance does start up I can call for heating at the same time and it all works fine. it is unlikely the pump fails intermittently. i.e. not creating the pressure rise
it could be a dodgy water sensor but until now (i had to drain it down in a hurry) it works ok on HW, at least most of the time.
I am minded that this is a water flow issue, iether through an air lock or something. it is a new system so unlikely to be a blockage but the heat load is approaching maximum
So, can anyone shed any light on this, is it a common fault or am i missing something,
It is plumbed into a sealed system with three zones, 1 x hw and 2 x CH.
On start up it has always been temperamental in that; if it starts on HW only chances are it will run ok and the HW system works as you would expect. there is an auto air vent on the flow to the cylinder
If it starts on any other zone, it will fail to start up quoting fault f75 (this means (no pressure rise was detected on turning on the pump) the cause in the manual states (water pressure sensor and or pump defective. too little water in appliance: connect external expansion vessel to return) I don't believe there is a need for an further expansion vessel as the pressure rise when hot is minimal.
I believe the pump works fine because when the appliance does start up I can call for heating at the same time and it all works fine. it is unlikely the pump fails intermittently. i.e. not creating the pressure rise
it could be a dodgy water sensor but until now (i had to drain it down in a hurry) it works ok on HW, at least most of the time.
I am minded that this is a water flow issue, iether through an air lock or something. it is a new system so unlikely to be a blockage but the heat load is approaching maximum
So, can anyone shed any light on this, is it a common fault or am i missing something,