FUSE KEEPS BLOWN ON MY BAXI 80 /105 COMBI

This topic originated from the Wiki page called Heating controls
Click here to return to the page called Heating controls.
Goto page 1, 2  Next
 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
  View previous topic :: View next topic  
Author Message
billyo

from United Kingdom

Joined: 20 Jul 2007
Posts: 1508
Location: Cumbria,
United Kingdom
Thanked: 0 times

PostPosted: Fri Jul 20, 2007 3:24 pm    Post Subject:
FUSE KEEPS BLOWN ON MY BAXI 80 /105 COMBI
Reply with quote Thanks

HI/GUYS NEED ADVICE I AM NOT A PLUMBER,BUT DONT WANT TO GET RIPPED OFF,GOT A BAXI 80/105 COMBI EVERY TIME YOU CALL FOR HOT WATER 2 AMP INTERAL FUSE GOSE BANG, BOILER WONT RUN WHEN YOU PUT IT TO HOT WATER AND RADIATORS , CANT GET A PLUMER FOR THREE DAYS
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
weareleeds

from United Kingdom

Joined: 13 Dec 2005
Posts: 655
Location: Yorkshire,
United Kingdom
Thanked: 0 times

PostPosted: Fri Jul 20, 2007 3:46 pm    Post Subject:
Reply with quote Thanks

Probably pump blowing fuses try disconnecting live to pump & see if it carries on blowing fuses
Back to top
 Alert Moderators
ChrisR

from United Kingdom

Joined: 24 Jul 2003
Posts: 18663
Location: London,
United Kingdom
Thanked: 62 times

PostPosted: Fri Jul 20, 2007 3:51 pm    Post Subject:
Reply with quote Thanks

BOILER WONT RUN WHEN YOU PUT IT TO HOT WATER AND RADIATORS

Turned the wall thermostat up?
If boiler then goes ok, look for water in HW microswitch. Don't know if that would blow a fuse though.

Turn power off, stick your head in and sniff - usually stinks of burning.
Back to top
 Alert Moderators
gas4you

from United Kingdom

Joined: 23 Feb 2007
Posts: 14312
Location: Norwich,
United Kingdom
Thanked: 41 times

PostPosted: Fri Jul 20, 2007 5:23 pm    Post Subject:
Re: FUSE KEEPS BLOWN ON MY BAXI 80 /105 COMBI
Reply with quote Thanks

billyo wrote:
HI/GUYS NEED ADVICE I AM NOT A PLUMBER,BUT DONT WANT TO GET RIPPED OFF,GOT A BAXI 80/105 COMBI EVERY TIME YOU CALL FOR HOT WATER 2 AMP INTERAL FUSE GOSE BANG, BOILER WONT RUN WHEN YOU PUT IT TO HOT WATER AND RADIATORS , CANT GET A PLUMER FOR THREE DAYS


Would help if you turned you're caps lock off icon_rolleyes.gif

__________________
Dave
DRL Gas Services
Back to top
 Alert Moderators
billyo

from United Kingdom

Joined: 20 Jul 2007
Posts: 1508
Location: Cumbria,
United Kingdom
Thanked: 0 times

PostPosted: Sat Jul 21, 2007 2:52 pm    Post Subject:
blown fuse 105 ebaxi
Reply with quote Thanks

hi, gas4you,
did as you said and took live wire of pump, this has stopped the fuse blown, panel ligths up green on water side when tap is running also red light at 60d, telling you pump has a fault .but if you put swicth on radiator and waterside just red ligth comes saying pump fualt, what next my knowledgeable friend.

best regards billyo
Back to top
 Alert Moderators
gas4you

from United Kingdom

Joined: 23 Feb 2007
Posts: 14312
Location: Norwich,
United Kingdom
Thanked: 41 times

PostPosted: Sat Jul 21, 2007 3:02 pm    Post Subject:
Reply with quote Thanks

Sounds like pump is shorting out as Weareleeds suggested.

__________________
Dave
DRL Gas Services
Back to top
 Alert Moderators
billyo

from United Kingdom

Joined: 20 Jul 2007
Posts: 1508
Location: Cumbria,
United Kingdom
Thanked: 0 times

PostPosted: Sat Jul 21, 2007 3:44 pm    Post Subject:
Reply with quote Thanks

weareleeds and gas4you,
thanks guys for your anwers, if pump is cause of fuse blown,as looks likely what can i do to fix it. can pump be repaired or do i bin it, would rather fix it if poss.

best regards
billyo
Back to top
 Alert Moderators
Dan_Robinson

from United Kingdom

Joined: 01 Jul 2007
Posts: 2396
Location: Hertfordshire,
United Kingdom
Thanked: 0 times

PostPosted: Sat Jul 21, 2007 3:53 pm    Post Subject:
Reply with quote Thanks

Replace with equivalvent model.

__________________
Regards

Dan Robinson

If I was right half as much as my wife was wrong I'd be a very happy man
Back to top
 Alert Moderators
clf-gas

from United Kingdom

Joined: 02 Mar 2007
Posts: 3063
Location: Lancashire,
United Kingdom
Thanked: 25 times

PostPosted: Sat Jul 21, 2007 3:57 pm    Post Subject:
Reply with quote Thanks

Get yourself down to the big shed and buy a replace ment pump.

Close valves either side of pump, issolate electric, place towel around the floor and remove old pump, only a bit of water.

remove wires from old and wire new as per, fit new to existing pipework and open valves, now turn electric back on on try boiler.

Well done chief the misses gets a bath you both put on the glad rags and paint the town red, she`s now got a new and pleased hubby icon_wink.gif

__________________
STUPID = Smart Talented Useful Person In Demand
Back to top
 Alert Moderators
namsag

from United Kingdom

Joined: 12 May 2004
Posts: 7929
Location: United Kingdom
Thanked: 59 times

PostPosted: Sat Jul 21, 2007 4:20 pm    Post Subject:
Reply with quote Thanks

As your boiler is a 105e ANY pump will not do . What you need if it is the pump causing the fault is a Grundfos 15/60 pump and just change the head of pump as the body is special to that boiler. And you will not find valves either side either as clf-gas said. You turn off boiler isolating valves
Back to top
 Alert Moderators
clf-gas

from United Kingdom

Joined: 02 Mar 2007
Posts: 3063
Location: Lancashire,
United Kingdom
Thanked: 25 times

PostPosted: Sat Jul 21, 2007 4:37 pm    Post Subject:
Reply with quote Thanks

Your right namsag,,,, I did`nt read the OP`s post properly. Was red misting at the time icon_mad.gif

Am calm now icon_wink.gif

__________________
STUPID = Smart Talented Useful Person In Demand
Back to top
 Alert Moderators
namsag

from United Kingdom

Joined: 12 May 2004
Posts: 7929
Location: United Kingdom
Thanked: 59 times

PostPosted: Sat Jul 21, 2007 4:45 pm    Post Subject:
Reply with quote Thanks

All been there CLF icon_redface.gif
Back to top
 Alert Moderators
billyo

from United Kingdom

Joined: 20 Jul 2007
Posts: 1508
Location: Cumbria,
United Kingdom
Thanked: 0 times

PostPosted: Sun Jul 22, 2007 4:04 pm    Post Subject:
Reply with quote Thanks

Nam-sag
thank you, i will be down plum-centre on monday.
clf-gas calm down and keep taking the tablets
every body who had an input to my problem slover a big thank you to you all, hope i can help you some time,

best regards billyo
Back to top
 Alert Moderators
billyo

from United Kingdom

Joined: 20 Jul 2007
Posts: 1508
Location: Cumbria,
United Kingdom
Thanked: 0 times

PostPosted: Mon Jul 23, 2007 2:28 pm    Post Subject:
Reply with quote Thanks

namsag be -aware just been took for a mug down our local plumbcenter in barrow in furness when in and bough 15/60 pump as you suggestet got it home and it is a completely differant unit one on my boiler is a 15/60 TF95 one he sold me is a 15/60 130 with a swicth on it mine is 3 bar this one is 10 bar, so took it back to man at PLUMCENTER THATS PLUMCENTER, AND NASTY MAN WOULD NOT TAKE IT BACK AS HE SAID I TOOK IT OUT OF ITS BOX,i said well who an i suppose to test it he said he had heard it all before and would kindly leave his PLUMCENTER i presume he would not like me to tell other people that if you buy and then open the box you cant excheange goods so all you guys be aware of opening goods from PLUMCENTER. BILLYO HAS BEEN RIPPED OFF
Back to top
 Alert Moderators
billyo

from United Kingdom

Joined: 20 Jul 2007
Posts: 1508
Location: Cumbria,
United Kingdom
Thanked: 0 times

PostPosted: Mon Jul 23, 2007 2:45 pm    Post Subject:
Reply with quote Thanks

billyo wrote:
namsag be -aware just been took for a mug down our local plumbcenter in barrow in furness when in and bough 15/60 pump as you suggestet got it home and it is a completely differant unit one on my boiler is a 15/60 TF95 one he sold me is a 15/60 130 with a swicth on it mine is 3 bar this one is 10 bar, so took it back to man at PLUMCENTER THATS PLUMCENTER, AND NASTY MAN WOULD NOT TAKE IT BACK AS HE SAID I TOOK IT OUT OF ITS BOX,i said well who an i suppose to test it he said he had heard it all before and would kindly leave his PLUMCENTER i presume he would not like me to tell other people that if you buy and then open the box you cant excheange goods so all you guys be aware of opening goods from PLUMCENTER. BILLYO HAS BEEN RIPPED OFF
icon_cry.gif
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Glow worm Ultimate 40FF boiler fuse F2 blown 7 2040 Thu Apr 05, 2007 9:08 pm
Fuse blown on a Modena 80e Boiler. 2 480 Tue Oct 10, 2006 7:46 am
Blown 3amp Fuse on Glow Worm Space Saver 10 1440 Mon Oct 08, 2007 9:42 am
vaillant turbomax 824... blown fuse? 3 280 Mon Jan 28, 2008 1:08 pm
Worcester - 24CDI - Blown fuse ?? Any advice appreciated! 3 1160 Mon Aug 07, 2006 7:14 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.