15Kw plus Cooker/hob and cable colours!

This topic originated from the How to page called Installing an electric cooker
Click here to return to the page called Installing an electric cooker.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
Cacus

from United Kingdom

Joined: 23 Jul 2007
Posts: 10
Location: Humberside,
United Kingdom
Thanked: 0 times

PostPosted: Mon Jul 23, 2007 12:58 pm    Post Subject:
15Kw plus Cooker/hob and cable colours!
Reply with quote Thanks

Hi all.

I am in the middle of a kitchen rip out and when removing a cupboard have found what I assume is the old cooker point (terminated thick cable - no switch or socket). Firstly the cable is almost an inch thick (and round) with three insulated cores Red, Blue, Yellow. Would I be correct in assuming that Red is live, blue is neutral and yellow is earth? As I\\\'d like to put a test meter on to see if it is still connected to the mains.

Secondly I\\\'ve been looking at a cooker and hob that\\\'s going to run into the 15Kw range (oven 7.4, hob 7.9 - maybe a bit more depending on which model we go for!), assuming that the cable is a minimum of 10mm (it\\\'s lot thicker than the one that went to shower!) would these be able to connect to the same point as I assume that these would have a draw of 65 Amps when on full (Like at christmas!).

Any advice would be appreciated.

Oh.. incidentally the consumer unit is a old Wylex plug-in job! Even if you can plug both in to the cable end would I be able to get a plug-in MCB with such a high rating?

Cheers
Steve
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Mon Jul 23, 2007 1:32 pm    Post Subject:
Reply with quote Thanks

if it is round, an inch thick, with red blue and yellow it sounds like a three-phase supply cable.

Hopefuly it is dead now but might carry 415volts.

It might have a steel wire armour round the three coloured cores.

Was your house ever industrial premises? this cable is not usually found inside houses.

the is a chance someone stole a length of cable from work and used it for some other purpose.

Wylex Standard consumer units with plug-in fuses or mcbs are not usually safe above 32A per circuit and often 60A max total of all circuits. Put up a photo of yours and we can say more.

If you are using a double oven and an electric hob you should supply each from a separate circuit. Have you considerd a gas hob?
Back to top
 Alert Moderators
Cacus

from United Kingdom

Joined: 23 Jul 2007
Posts: 10
Location: Humberside,
United Kingdom
Thanked: 0 times

PostPosted: Mon Jul 23, 2007 2:22 pm    Post Subject:
Reply with quote Thanks

Thanks for the quick reply.

The house is a terraced built 1910 and so never used industrially. It's not armoured cable but the grey outer jacket is rubbery (like flex) though much thicker. Also the internal cores of each cable consist of half a dozen thick copper strands (like armoured). - I'm at work at the moment but will try to up a pic of cable and fuse box.

Have considered gas hobs but ceramic is so much easier to clean!! LOL
Back to top
 Alert Moderators
Chivers7

from United Kingdom

Joined: 17 Jan 2007
Posts: 276
Location: Surrey,
United Kingdom
Thanked: 0 times

PostPosted: Mon Jul 23, 2007 3:24 pm    Post Subject:
Reply with quote Thanks

sounds like VIR? you might have to run a new cable in
Back to top
 Alert Moderators
Cacus

from United Kingdom

Joined: 23 Jul 2007
Posts: 10
Location: Humberside,
United Kingdom
Thanked: 0 times

PostPosted: Mon Jul 23, 2007 5:11 pm    Post Subject:
Reply with quote Thanks

Firstly my estimate of cable thickness was on the big side it's more like 20mm in diameter.

I have (hopefully) enclosed a pic of the fuse box and cable.

Assuming that with the appropriate MCB in the right slot there is power to the cable would it be best to only have the 7.4kw oven on this and go for the gas hob. And of cause does the fuse box look ok for the 45amp mcb?







By the way did I assume correctly about the core colours?
Back to top
 Alert Moderators
JohnD

from United Kingdom

Joined: 15 Nov 2005
Posts: 24037
Location: Hampshire,
United Kingdom
Thanked: 54 times

PostPosted: Mon Jul 23, 2007 5:13 pm    Post Subject:
Reply with quote Thanks

can't see the pictures

edited

I can see them now


1) that is a very old CU. the max load it can carry is 60Amps. It is overdue for replacement.

2) the max fuse or MCB it will accept is 32Amps (unless it has been bodged)

3) that cable termination is disgusting. Assume you can't use it and budget for a new circuit.

p.s. if/when you take off the cover of that CU, there will still be live terminals exposed at the top of the main switch, even when you have turned it off.

p.p.s. As i suspected, someone has used an unsuitable length of cable they stole from work.
Back to top
 Alert Moderators
Cacus

from United Kingdom

Joined: 23 Jul 2007
Posts: 10
Location: Humberside,
United Kingdom
Thanked: 0 times

PostPosted: Mon Jul 23, 2007 7:02 pm    Post Subject:
Reply with quote Thanks

Thanks for the advice.

Will get some quotes for a new CU and run, though due to the added expense of a new CU may just stick with a all gas oven.

Thanks anyway.
Back to top
 Alert Moderators
Steve

from United Kingdom

Joined: 15 Apr 2005
Posts: 12845
Location: Yorkshire,
United Kingdom
Thanked: 21 times

PostPosted: Mon Jul 23, 2007 7:39 pm    Post Subject:
Reply with quote Thanks

the CU needs replacing anyway. You will probably find it has a wooden frame back. icon_eek.gif
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
2.15kw to a 32amp cooker unit ??? 15 740 Tue Dec 06, 2005 5:27 pm
Wiring for a 15kW oven 9 340 Thu Feb 05, 2009 4:53 pm
New Harmonised Cable colours & B&Q etc 3 520 Fri Apr 15, 2005 2:27 pm
Old and new cable colours. 4 240 Mon Mar 30, 2009 9:25 am
Cable colours? 6 420 Thu Jun 02, 2005 5:01 pm