PutUmUp

from United Kingdom

Joined: 18 May 2004
Posts: 2
Location: United Kingdom
Thanked: 0 times

PostPosted: Tue May 18, 2004 8:42 am    Post Subject:
New Ring main help?
Reply with quote Thanks

I\\\'ve just run a new ring main for my kitchen, there are nine double 13amp sockets,when i made it live it was all ok and didnt trip out, but the second i plug ANYthing in it trips. Is due to a short or the MCB is to small in amps??
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
breezer

from United Kingdom

Joined: 03 Jan 2003
Posts: 23346
Location: Sussex,
United Kingdom
Thanked: 5 times

PostPosted: Tue May 18, 2004 9:34 am    Post Subject:
Reply with quote Thanks

is it the rcd that trips?

__________________
Do you like music Mr Finch?
Forum = Opinions
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16485
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Tue May 18, 2004 9:51 am    Post Subject:
Reply with quote Thanks

And is it the same appliance you are plugging in each time?

What size is the MCB? And do the appliances work when plugged in elsewhere?

Is there lots of damp plaster around?
Back to top
 Alert Moderators
breezer

from United Kingdom

Joined: 03 Jan 2003
Posts: 23346
Location: Sussex,
United Kingdom
Thanked: 5 times

PostPosted: Tue May 18, 2004 9:54 am    Post Subject:
Reply with quote Thanks

securespark, the poster said but the second i plug ANYthing in it trips so i should say a variety of items have been tried. my guess is n + E reversal

which is why i figure the rcd is tripping

__________________
Do you like music Mr Finch?
Forum = Opinions
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Tue May 18, 2004 12:47 pm    Post Subject:
Reply with quote Thanks

He also said "new ring main", so if it's a split-load board the neutrals could be going to the wrong side...

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16485
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Tue May 18, 2004 3:19 pm    Post Subject:
Reply with quote Thanks

Alright, alright, you bunch of f*cking Sherlocks!!!!

icon_lol.gif
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16485
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Tue May 18, 2004 3:22 pm    Post Subject:
Reply with quote Thanks

It's over to PutUmUp, The only Red Indian kitchen fitter in the UK!! No offence....
Back to top
 Alert Moderators
PutUmUp

from United Kingdom

Joined: 18 May 2004
Posts: 2
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed May 19, 2004 4:00 pm    Post Subject:
Reply with quote Thanks

breezer wrote:
is it the rcd that trips?
It is the RCD that trips, i've disconnected every thing, and started again from start, adding on socket at a time, but no change . so i connect the ring to a socket that i know is fine ((in another room via a extension,so i could see if there was a problem with wiring i had ran) and everything works fine, the second i reconnect to the MCB the RCD trips when i switch a device on. I have checked and double check the cables are to the right terminals, and that there is no shorts, it trips even when i created a radial with one socket on the end. thanx for all the help.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16485
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Wed May 19, 2004 7:22 pm    Post Subject:
Reply with quote Thanks

Is there any damp about??
Back to top
 Alert Moderators
BR

from Ireland

Joined: 31 Dec 2003
Posts: 334
Location: Ireland
Thanked: 0 times

PostPosted: Wed May 19, 2004 9:12 pm    Post Subject:
Reply with quote Thanks

damp on the brain!! icon_smile.gif My bet is that he connected the neutral to the wrong block in the CU. N/E reversal seems less likely.
Back to top
 Alert Moderators
ban-all-sheds

from United Kingdom

Joined: 27 Aug 2003
Posts: 21990
Location: London,
United Kingdom
Thanked: 78 times

PostPosted: Thu May 20, 2004 12:30 am    Post Subject:
Reply with quote Thanks

I said it first. Baggsy the prize if it's right. Feet-shuffling and spreading the blame if it's not....

__________________
I mustn't warn people that the "experts" on the plumbing forum can't be trusted to tell the truth.
Back to top
 Alert Moderators
securespark

from United Kingdom

Joined: 11 Jan 2004
Posts: 16485
Location: Cheshire,
United Kingdom
Thanked: 14 times

PostPosted: Fri May 21, 2004 2:34 am    Post Subject:
Reply with quote Thanks

Actuellement, I was called out to a new-build at 3 am one morning to find a dejected young woman (Wa-hey!!) whose RCD had tripped. Spent hours trying to trace how, why, where and when. Failed miserably.

Turned out the walls were a smidge damp and this was having funny effects on the rcd. That's Wylex for you.......
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Diagnosing a ring main installation 8 400 Mon Mar 17, 2008 12:38 pm
Adding sockets to a ring main 9 1120 Sun Aug 13, 2006 9:09 pm
spurs on a ring main? 2 300 Fri Mar 21, 2008 5:43 pm
Extending Ring Main 2 460 Fri Aug 18, 2006 7:57 pm
Upstairs ring main tripping RCD 8 460 Tue Mar 11, 2008 10:10 am