Mains Voltage Spot Cable Size?

This topic originated from the How to page called Choosing the correct size cable
Click here to return to the page called Choosing the correct size cable.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK
  View previous topic :: View next topic  
Author Message
will.ardill

from United Kingdom

Joined: 02 Aug 2007
Posts: 2
Location: United Kingdom
Thanked: 0 times

PostPosted: Thu Aug 02, 2007 8:38 am    Post Subject:
Mains Voltage Spot Cable Size?
Reply with quote Thanks

Dear Forum,

I am installing 9no. 50W mains voltage holgen spots in an open plan living / dining room ceiling. I have used 1.5mm2 two core and earth for the lighting circuit generally. I am proposing to use .75mm2 two core flex to daisy chain between fittings. Is this acceptable? Your comments would be very much appreciated. Thanks in advance.

Will
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
RF Lighting

from United Kingdom

Joined: 31 Mar 2006
Posts: 10752
Location: Birmingham,
United Kingdom
Thanked: 73 times

PostPosted: Thu Aug 02, 2007 5:24 pm    Post Subject:
Reply with quote Thanks

Why not just keep it in 1.5mm˛ like the rest of the circuit?

__________________
I downlights
Back to top
 Alert Moderators
sparkmanc

from United Kingdom

Joined: 28 Jul 2007
Posts: 61
Location: Lancashire,
United Kingdom
Thanked: 0 times

PostPosted: Thu Aug 02, 2007 5:29 pm    Post Subject:
Re: Mains Voltage Spot Cable Size?
Reply with quote Thanks

will.ardill wrote:
Dear Forum,

I am installing 9no. 50W mains voltage holgen spots in an open plan living / dining room ceiling. I have used 1.5mm2 two core and earth for the lighting circuit generally. I am proposing to use .75mm2 two core flex to daisy chain between fittings. Is this acceptable? Your comments would be very much appreciated. Thanks in advance.

Will


Agree with RF, the phrase "generally used 1.5 twin" concerns me however. What other cable did you use?
Back to top
 Alert Moderators
will.ardill

from United Kingdom

Joined: 02 Aug 2007
Posts: 2
Location: United Kingdom
Thanked: 0 times

PostPosted: Sat Aug 04, 2007 8:27 am    Post Subject:
Thanks
Reply with quote Thanks

Thanks Guys,

I will continue with the 1.5mm2.

Sorry about the misleading 'generally'! I have used 1.5mm2 everywhere else.

Ta

Will
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Electrics UK All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
Fire rated low voltage spot lights 6 260 Mon Jul 07, 2008 9:53 am
Low Voltage Spot Lights 2 420 Thu Dec 21, 2006 11:08 am
Simple Low Voltage Spot Lights Question 2 280 Fri Feb 08, 2008 6:26 pm
Low voltage halogens spot for a ensuite 3 320 Sun Nov 19, 2006 11:56 am
Mixing types of spot light 3 200 Wed Jul 16, 2008 8:52 pm



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.