shower cable size
27 Jun 2007
Cheshire
got a 10.5 kw shower to fit.comes in at 45.65 amps. looking at the on site guide for CCC. 10mm cable ref method 4 says it will carry 43 amps. table 6E1.
so am i looking at the correct table? or can i assume that some
of the cable will be buried in the wall and some will be clipped
direct and so it will up the CCC to a sufficient amount?
Firstly, the 10.5kW rating is for 240V not 230 so it will actually draw 43.75A @ 240V and less if your voltage is lower.
10mm² t&e clipped direct can take 64A. 47A when installed directly in an insulated wall and 44A when in conduit in insulated wall. *From table 4D5A of BS7671.
If you give is a run down of all the environments the cable will run through then we can tell you for definite whether 10mm² will do.
u mean less if the voltage is higher? cable runs about 3 metres ref 4 and then clipped method 1 for about 6 metres
Do we have to go back to basic Ohm's law...... ;)
For a fixed resistive load (eg a heating element), it will draw more current at 240V than at 230V
Check the rating plate to see if the Kw rating is at 240V or 230V
10500/240=43.75A
10500/230=45.65A
GaryMo said:
10500/240=43.75A
10500/230=45.65A
No.
A shower that is rated at 10.5kW @ 240V has a fixed resistance of: 240v / 43.75A = 5.49 ohms.
If you run that same shower at 230v: 230v / 5.49ohms = 41.9A or 9.6kW.
Which is why you have to see if the shower power rating is based on 230 or 240V to determine it's current draw ;)