Relationship of MCB size to cable size
Note - this considers overload protection only. Other factors such as voltage drop and disconnection times need to be considered when designing a circuit. Also, it only quotes the example tripping/non-tripping currents for Type B MCBs, not cartridge or rewirable fuses, which are not the same.
Protective devices have 3 values of interest here:
In: its nominal rating (e.g. 32A) I1: its non-fusing/non-tripping current. For a Type B MCB this is 1.13In I2: its fusing/tripping current. For a Type B MCB this is 1.45In, and it must trip within 1 hour
So if we have a circuit whose design current (i.e. the current that it is expected to carry in normal use) is Ib, then this should not be greater than the rating of the protective device:
Ib ≤ In
If Iz is the current-carrying capacity of the cable for continuous service allowing for the way that it has been installed, then this must be no less than the rating of the device:
In ≤ Iz
Finally, 1.45 times the current carrying capacity Iz of the cable must be no less than I2, the current causing effective operation of the device:
1.45Iz ≥ I2
So Ib ≤ In ≤ Iz
and
I2 ≤ 1.45Iz.
Or if you prefer pictures:
Running an MCB at or near its limit for long periods will cause it to overheat, and eventually weaken. But you shouldn't do that - look at the diagram, Ib is lower than all the rest.
Related forum topics
No forum comments / questions currently relate to this article.
Add a comment or question about
this article in the forum:
Your comment or question:
First,
Existing users click here to log in.
New users click here to join FREE!
Then,
 Subject:
 Comment:
electrics/fuses_and_miniature_circuit_breakers/mcbtocable.txt · Last modified: 2007/09/12 09:18 (external edit)
DIYnot.com
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum | Shop
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.
Copyright © 2000-2008 DIYnot Limited. All rights reserved. Reproduction in whole or in part in any form or medium without express written permission of DIYnot Limited is prohibited.