Unless you read the O2 and excess air off the analiser printout how can you possibly know the figures. :rolleyes:[/quote]
Experience? :D
Why can't you guys be helpful, or just shut up?
These figures were read from a flue gas analyser. They are good.
CO2 and O2 vary inversely with each other, and it is usually the oxygen value which is measured nowadays, although in the past carbon dioxide was measured with wet analysers. That is why both figures are in use.
Carbon monoxide at 1% in air is indeed fatal, but the analyser is measuring the concentration in the flue gas, not the air in the room, and the figure quoted is OK.
will you explain it or not? .
I'll try to explain so here goes , will await the bashing. :D
Some will argue that O2% can't be calcuated from CO2% , reason being how do we know whether CO2% is on the left (fuel rich) or right (fuel lean) side of the stoichiometric combustion bell chart , well we don't , then again if CO2 @ 6.5% were on the fuel/rich side of the curve CO would be in excess of 30000ppm (3%) , in the case here we know CO to be pretty low (64ppm) with a CO/CO2 ratio of 0.0006 , so with this in mind we can safely say combustion is fuel/lean , this being the case O2/Xs air can be sought from CO2% of flue gas.
Calc...........
9.4% CO2 X 20.9 = 196.46/11.9 (co2max)= 16.509....20.9-16.509 = 4.3 O2%/26% Xsair.
Above calc is the reversal of CO2max/CO2
CO2 = 11.9 (co2max) X (20.9 - 4.3)
------------------------------------------------- = 9.4%
20.9
..........& failing this seek FGA readings. :cool: :D
:rolleyes:
OP, if you haven't already jumped off a cliff!! I would definate recommend a magnet filter be fitted to the return from the central heating and like already posted by someone else,I prefer the Fernox TF1 as well £85 plus Vat is what i'm currently paying for them then i would charge £50 to fit if local
Thanks all for your input and happy now that the figures confirm my boiler is running efficiently.
As for the filter, whenever I do any DIY on the radiators the water is always clear so I will defer for now any decision on fitting one.
One other point - 'inhibitor' was put in the system during boiler installation, but as I have partially drained the system to fit a couple of TRVs, is there a DIY method of measuring the level of inhibitor remaining in the system?
Cheers - Doug
My Worcester Bosch Greenstar 35 Combi boiler has just been serviced under an annual Homecare agreement
Boiler was not serviced but checked for safe operation. Look at the manual and you will realise what a service entails.
DP - I do appreciate the difference, and am of the opinion that "if it works.....don't fix it". As the boiler has been monitored to be running efficiently, then that will do for me. :D