Hi can you please throw some light on this problem
Switch the boiler on the fan starts & continues boiler doesn't even try to fire
I've checked the coil all's ok I've ordered a new photocell but usually if the photocell is dirty the boiler goes to lockout
This doesn't go to lockout the fan still whirrs until I kill the power any ideas? Please
Cheers Paul
 
Sponsored Links
Thanks for the reply any ideas why the lockout light didn't come on
 
The cell should see dark during pre purge.
If it is faulty and thinks it sees light then the box stays in pre purge mode.
 
Sponsored Links
Ahh right that's shed some light on this (excuse the pun)
Thanks for the explanation
 
Unplug the photo cell (electrically) and see if it fires up after 12 secs..and then locks out.
 