Wonder if anyone can help, my cooker suddenly switched off so logically I went to the fuse box to see what tripped, To my surprise NOTHING had tripped, I had surely expected the 40amp mcb to have tripped so is there something wrong with the mcb despite not tripping? I am puzzled. Is this even common, l t me know guys.
 
Sponsored Links
Might be a loose connection somewhere I would start at the cooker switch, power off of course
 
Some MCBs don't have much of a visual trip indication- have you tried pushing the MCB to the OFF position then back ON? Is there an RCD covering that block of your consumer unit? Is that still ON? After that you're into some detective work- is the cooker hardwired (via a cooker switch) or is there a 13A plug somewhere in the circuit? Does the entire cooker not work or is it just the oven or rings that don't work?
 
Yes I tried switching on mcb on off also the rcd circuit has not tripped i checked the terminal block behind cooker, there's no voltage reading despite the mcb in ON position it's baffling me
 
Sponsored Links
Do you have a switch somewhere? might be hidden in a kitchen unit, what are you using to test for voltage?
 
Last edited:
Did you meter live to earth as well as live to neutral at that terminal block? Does sound like a loose connection somewhere, time to knock the power off and check the whole circuit.
 
Yes I tried switching on mcb on off also the rcd circuit has not tripped i checked the terminal block behind cooker, there's no voltage reading despite the mcb in ON position it's baffling me
Ok. But have you done the obvious test:
Is there voltage leaving the MCB itself?
 
there's no other switches behind the cooker only the cooker socket outlet which I tested with a multimeter for voltage across live and neutral with mcb ON but no voltage detected so obviously theres no current flowing from mcb to this point? I haven't actually tested from the fusebox to see if voltage is leaving the mcb, ill check that tonight after work, thanks for your help so far, will keep you posted.
 
....... I tested with a multimeter for voltage across live and neutral with mcb ON but no voltage detected so obviously theres no current flowing from mcb to this point? ....
You need to understand the difference between CURRENT and VOLTAGE

The only time that you will get CURRENT is if there is a LOAD on the circuit (a cooker in your case).

You need to test for VOLTAGE only, at this stage. Take a logical approach. Start at the supply source (consumer unit). Check voltage out of the MCB. If voltage is there, then its time to look elsewhere.

Also, always test between line and neutral and also between line and earth.
Don't forget that if the neutral is missing/faulty then the live will APPEAR not to be present(y).
 
Sorry I meant to say voltage NOT current, my bad, anyway I’ve just checked the voltage at the mcb and it’s ok so it seems the mcb is not faulty, I need to look elswhere now as you guys have suggested, I’m going to try and check for any loose connections on Saturday as it’s late now. Thanks guys. I must add that this was wired up when I had a new kitchen extension done so I might find it hard to trace exactly where this wire is going and if it’s connected t something else?
 
Oh by the way when you say also test the connection between live and earth, and live and neutral what readings am I supposed to get with the mcb switched on or off, is it the same as checking the voltage across live and neutral, I know silly question but I don’t want fireworks let me know please cheers.
 
With MCB off, there should be 0V from L out (top) to N and E.

MCB on, L to N and L to E should both be around 240 V.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back