The breaker is there to protect the cabling, not the appliance. The breaker size is selected once the cable size is known. The cable size is selected once the load is known (plus other factors, like cable run inside insulation, etc).

mind you, the regulations say that one should take account of the Manufacturer’s Instructions, so it may be prudent to install a (for example) 16A breaker if that is what the MIs mandate.
 
Sponsored Links
The breaker is there to protect the cabling, not the appliance. The breaker size is selected once the cable size is known. The cable size is selected once the load is known (plus other factors, like cable run inside insulation, etc).

mind you, the regulations say that one should take account of the Manufacturer’s Instructions, so it may be prudent to install a (for example) 16A breaker if that is what the MIs mandate.

Manufacturers instructions are often wrong.
So take account of but don’t blindly follow.
 
Sponsored Links
Not mandatory - but most people would fit a 32A.

Your 20A will be acceptable using what we call 'diversity' for cooking appliances.

That is the first 10A plus 30% of the remainder.

6.4kW @ 240V = 26.7A.
so 10 + (16.7 x 0.3) = 15A.
 
Spoke to an electrician earlier, he's coming to have a look tomorrow. But he says it needs a 6mm feed.

Am I doing to get the same response from all electricians?
 
I think the guidance notes say 6mm for cooker, so i guess many would include an oven. But the people on here have designed the specific circuit according to the load so those rules of thumb are overly conservative in that case.
 
Spoke to an electrician earlier, he's coming to have a look tomorrow. But he says it needs a 6mm feed.

Am I doing to get the same response from all electricians?
You very well might.

6mm² had to be used for 30A cooker circuits in the past with rewirable fuses.
People still use it because it has always been used so people still use it because it has always been used.

See if you can find an electrician who knows what he is doing.
 